Hello – our house is from the ‘40s but “new to us”, so still learning about its quirks as we go. We just had someone replace a chimney rain cap, but while he was up there he noticed condensation damage on the chimney liner.
It looks like our boiler (ECR International CHB-100) and water heater (Giant UG50-40LF-N2U) both vent through that flue. The chimney guy said that the boiler exhaust may be set up incorrectly and should be venting out through the wall instead, in which case we’d need a smaller chimney liner for the water heater only. He said the current setup also gets in the way of easily replacing the chimney liner, and strongly recommended having an HVAC specialist take a look at it.
(Please excuse the mess.) We’re going to have someone in to look it over, but wanted to learn a bit in advance so we can understand the issue better. One thing that may be confusing the issue is that the chimney guy assumed it was a Category IV condensing boiler, but the information I can find for the model online indicates mid-efficiency (AFUE 85%), non-condensing with instructions for either Category I or III venting, while the pre-move inspection report simply says high-efficiency with forced draft venting.
Is the venting set up wrong? What questions should we be asking / information should we be providing when the technician comes? Thank you for any advice you can provide.
Comments
-
Without looking at the I&O manual for the boiler, I think you should definitely should be venting it through the wall with the appropriate piping (check the manual). Even if it's not a condensing boiler, the flue gas temperature may be too low, and definitely too low by the time it reaches the top of the chimney.
Is the chimney exterior (3 sides exposed to the elements)?
Your water heating venting is suspect. When you fix the boiler, come off the top of the water heater higher with the vent, then elbow, and use the hole previously used by the boiler.
I think all your condensation is from the boiler.
If you can get a chimney contractor to bless your liner, I'd leave it alone. You don't need a smaller liner for a water heater. It's the same size liner you have been using when heat isn't calling, and all summer for hot water.1 -
Your reading of the boiler is right. The ECR install manual for the CHB series says these are Category I and Category III boilers, so it can vent into the chimney as Category I or out the side wall as Category III. It isn't a Category IV condensing boiler, so chimney venting isn't wrong for it by itself. Whether it's set up right is the question.
The two setups have different rules. Into the chimney, the manual calls for a 3" x 4" increaser at the boiler outlet, a lined chimney, and the connector sized from the NFPA 54 vent tables. Out the wall as Category III, it gets its own AL29-4C stainless vent and nothing else connects to it. One thing to ask about directly: the manual's chimney section is oddly worded on sharing a flue with another appliance (one line says common venting isn't allowed, the next says the boiler and other appliances can share a chimney per the vent tables), so have the tech tell you how he reads it for your setup.
The condensation fits too. The manual itself says these boilers run lower stack temperatures, and it says an outside chimney shouldn't be used unless it's lined or enclosed in a chase. Cooler flue gas in a liner that's too big or too cold is how you get condensate.
Questions I'd ask: which category is it installed as right now, and does it match the manual? What size and type is the liner, and was it sized for both appliances together? Is the chimney on an outside wall? If the boiler goes out the wall, what liner size does the water heater need alone? The manual itself warns that a flue left with fewer appliances is likely too big for the ones that remain, which is what your chimney guy meant. And ask for a draft and CO check on the water heater and a combustion test on the boiler once it's done.
To have ready: model and serial numbers off both rating plates, the chimney guy's photos of the liner damage, and the inspection report.
0 -
Thank you both - the chimney is on an exterior wall and quite tall, so that makes sense about the condensation. We'll look into the water heater venting as well, and the questions are very helpful.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 136 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements