Precharge of RO System Storage Tank

Options
mattmia2
mattmia2 Posts: 18,459

I have a reverse osmosis system that is about 30 years old and the storage tank has lost its charge again. What is the proper precharge for these? I charged it to 40 psig thinking that was about the municipal water system pressure and it held about 1 glass full of water. I let charge out until it started filling and that was still too much. How do I know what to charge it to?

Comments

  • hot_rod
    hot_rod Posts: 28,798

    5-7 psi is typical

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream