Zone issue
Hi when the system was installed I asked for a second zone option for an unfinished second floor. I finished the second floor added the zone piping and thermostat. It works when the thermostat calls for heat but it also works when the first zone calls for heat. So I disconnected the new thermostat upstairs and just throttle down the flow to the upstairs by closing the ball valve till I found the right balance. Now I would like to use that second circulator to add an indirect heat tank. The first floor is on a TECO 0015 mfs3 circulator which flows through the boiler. Right now flow goes out through a manifold to the first floor and the second support of the manifold goes to the upstairs. Can I ter off of the first floor tubing and add the second floor to that with a ball valve to keep the throttle at the right point and then rejoin the return line with another tee? That would free up the second zone for the indirect heater. That zone uses a taco 007 f5/5 circulator. If I can do it would seem I would need a flow check valve or zone valves to keep either zone from bleeding into the other. Circulators are on a Taco Sr 502.
Does that make sense? I'm not a plumber/heating guy just a homeowner who likes to learn how to do things. Thanks
Comments
-
Sounds like you're getting unwanted flow through the upstairs circuit whenever the first floor circulator runs. I'd investigate that before changing the piping around.
If both floors are connected to the same supply and return manifolds, simply switching off the second circulator won't necessarily stop water flowing through that loop. Depending on the piping arrangement, you'd normally need properly positioned flow checks or zone valves to prevent unwanted circulation.
Combining both floors onto one circulator is possible, but balancing them with a partially closed ball valve isn't really ideal. The circulator needs to provide enough flow for both circuits, and the flow distribution could change if you make further modifications.
For the indirect tank, I'd also check how the Taco SR502 is wired and whether the boiler control can provide domestic hot water priority.
Before repiping anything, could you confirm whether there are currently any flow-check valves fitted, either separately or built into the circulators? A simple piping diagram would help quite a bit.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 135 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 52 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements