Failed Fall Startup - McDonnel & Miller #67 – Float Type Low Water Cutoff
Tried to fire up our Dunkirk 400 steam boiler, but failed.
I can hear the electronic ignition trying to fire. I then usually hear a "thunk" as the gas valve opens, and then the burners fire up.
However, I cannot even get to the "thunk" step this year. I assume my low-water cut off is my first safety to check. (McDonnel & Miller #67 – Float Type Low Water Cutoff) I have water in the boiler at the proper level. I have removed the float access plug at the top and moved the float. (I believe it was stuck before I applied a little pressure with a punch.) It is not draining as cleanly as I would like, so it may have some debris.
Question for the forum experts: Is there a way to bypass the LWCO just for testing purposes? (For example, can I just touch the red wire and white wire at the float switch control, and then try to fire the boiler and determine if my gas valve will open?)
My #67 series LWCO is seven years old. If I can prove it is the problem, then I think I should probably just replace it. (However, I am currently broke, so trying to start/fix boiler DIY on a minimal budget.)
Thanks for any assistance or advice! (Please phrase answers at about the level of a moderately handy homeowner.)
BUT ONLY TO TEST. Do not under any circumstances jump the LWCO to get heat. You run the risk of a fire or cooking the boiler.
You can buy the gaskets and take the #67 apart to clean it it will be messy and difficult but will save you $$$. McDonnell Miller recommends replacement after 10 years but may just clean them. Parts from MM and a replacement are expensive.
1 -
Thanks Ed.
It looks like your main point is to "idiot proof" a safety issue. Yes, I agree - if I can bypass I just want to test my system components, but will NOT RUN FOR HEATING.
Will touching the two wires actually work to send the signal to the gas valve safety switch?
P.S. Once I make the decision that the LWCO probably needs to be replaced, I am much more confident in taking it apart and cleaning. "If it ain't broke don't fix it. If it is broke, you can at least try to fix it."
Dang it, that didn't work.
I hate trying to identify electrical problems. If I put circuit tester on those wires, should it show a few millivolts? AC or DC?
Or should I just get a positive signal when checking the continuity?
Typically the wiring would have the M&M 67 cut off power to the ignition module. So hearing the ignition module trying to do its thing it does not sound like an M&M 67 issue to me.
Does the pilot light when the ignition attempt is made ?
If I had to point a finger at something from here I'd suspect a contaminated flame sensor (if it has one) or igniter rod, ignition module, wiring to the gas valve or the gas valve. Depending on if the pilot actually lights or not.
All depends on the system type DC Millivolt or 24 VAC. Since you have an ignition module I suspect it would be 100% 24 VAC electrical control.
Is Dunkirk 400 the correct Make and Model, I can't find any data on it.
One Pipe System0 -
This is my actual model. Dunkirk – Model: D247-400 (400,000 BTU/hr)
I don't think I have a traditional pilot light? In my non-expert analysis, when the thermostat signals to turn the heat on, the electronic igniters start firing. (I can hear noises at the burner tubes.) The gas valve then opens (with a loud "thunk"), and the burners are then ignited a second or two later.
The gas valve does NOT open when I have a "safety switch" sending a signal to the controller (or gas valve) that it is not safe to fire up the boiler. (If my description is incorrect, or incomplete, anyone please feel free to clarify.) I believe my electronic igniters do try to fire even when one of my safeties (LWCO, high pressure, etc.) operates by telling the gas valve not to open? THAT is the step that the safeties prevent.
P.S. I do have an insert fireplace and understand fairly well how a flame sensor thermocouple prevents the gas valve from opening when the pilot light is not on. I occasionally fail on that fall start-up by not holding the pilot light fire on long enough to heat the thermocouple above the safety level before I turn the gas valve control to the "on" position.
I do not believe my Dunkirk boiler has an analogous safety switch. In my (non-expert) opinion, the burners will fire up without any previous heat being applied to the safety switches.
Thanks.
This is the wiring diagram for the Steam D247. The IP (Ignition Control module) and MV, MP, PV connections to the gas valve on the diagram is the end of the electrical line. If Ignition Control module is sparking all the safeties and limits are in their normal state providing power to the Ignition Control module. 24 VAC to the Ignition Control module starts an internal sequence of events to light the main burner.
Spark, open the PV (Pilot valve), prove there is pilot flame. Then if the module is happy with the pilot flame proof then the MV (Main Valve) opens letting the burner light. If the sequence is not completed properly, it stops, then shuts every down and it may retry again.
This method / system is not a thermocouple based safety and does not use a thermocouple. It uses flame rectification the detect the presence of the flame, not heat.
Take a closer look at the equipment.
One Pipe System0 -
Modern gas steam boilers will have several safety limits wired in series before the burner . Some you can reset , some you may have to replace and some need to be cleaned (pigtail) .. I wouldn't waste the time guessing . What is needed is a voltage meter to find the break . Check across each limit until you find voltage . Most gas boilers will be running 27V ….
The diagram shows 3 controls to start the boiler and they all have to be calling for heat (contacts in the closed position). Thermostat, low water cutoff, high limit (pressure control for steam/aqustat for hot water and an additional pressure control/aqustat optional manual reset limit.
TH-1 thermostat, LWCO -low water cutoff, ps/HL is limit control, and optional ps/hl manual reset.
- 135 Chimneys & Flues
- 16.2K Strictly Steam