Gallons of foam from bleeder, zero air in tigerloop
Have a 5yrold cmf2 80. 40ft of 3/8 to outdoor 275 gallon vertical tank. Top drawl suction line Tank-firomatic- webster osv- drop 5ft to ground- 40ft run - firomatic with tigerloop ultra.
3 weeks ago furnace started right up. Ran for 5hrs, shut it off at 5am. 2days later it wouldn't start. I bled the line. About 2 quarts of foamy water came out. I checked the exterior line, found a cracked flare nut fitting on a union. I reflared and replaced all conections. I dipstick checked the tank, 129 gallons, no water detected. I bled the line..intermittent oil, thrn all foam. 5 gallons, still foam. 2 days ago, i installed tigerloop. Bled the lines still foamy but no air.. not 1 bubble in the tigerloop. Blef another 2 gallons, line seems clear. Furnace wont fire up. Checked gun box assembly. Right Electrode covered in carbon. Cleaned and buffed woth emery board. Checked nozzel, all clear. Furnace wont fire up. Bled the line.. ALLLĹ FOAMY, 5 gallons all foamy.
Pleasssssse help. Its going down to 27 on Tuesday night and this is our only heat.
Comments
-
Try to tap the tiger loop with a block of wood to get the float to free float. It is stuck on an angle and a good swift kick will set the internal valve free.
OR
a leak has developed in the fuel line somewhere.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
I just read the rest of your description and learned that you have water in your fuel. That is a real problem. Checking the fuel condition is more important than anything else.
When you use water-finding paste to check for water in the fuel, you must wait 30 seconds for the paste to change color from contact with the water. Then you must read the water paste right away. I have had water-in-fuel readings that did not show up with water paste because I didn't let the paste soak up the water for 30 seconds or more. It is not an in-and-out test.
Is this a steel tank with a bottom valve or bottom plug? You need to let some liquid out of that bottom opening to see if it is fuel or water.
You can also use a temporary 5-gallon pail to hold the oil. Then connect a temporary fuel line from the 5-gallon pail to the burner through the Tigerloop. The oil filter has some water in it, so get a new spin-on filter and start fresh. Once you have the burner operating from the temporary 5-gallon pail, you have proof that the burner and its fuel supply setup are working.
Next, use a separate pump to draw fuel from the tank into a container to see if there is water in the fuel near the bottom of the tank. At some point, you will find where the problem is as you eliminate each section of the temporary setup that works and reconnect the parts of the permanent system until it fails.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
The 40ft, 3/8 oil line, fuel tank, firomatic, osv, everything installed new last fall. When i pulled 2 quarts of water out of the line i found a cracked fitting. . I wanted a valve on the bottom of the tank but peope said it could crack so i put a plug in. Ill drain some like u suggested in the am. Ive used the paste ona few of thr buckets of fuel ive got from the bleeds, its all been clean of water. ( i hoped the cracked fitting pulled condensate into the line and that was the extent of the water contamination) my yr has been so crap. The tigerloop is new.. like 2 days new. How do i know if the float is stuck? The bottom chamber float or the top? One more question . Is it possible tbe pump is siphoning air? no air or foam in the tigerloop but straight gallons of foam at the bleeder? Bad gasket or something. I was pulling foam before installed the tigerloop. So i dont think the bypass plug or return line, could be thr cause.
0 -
-
OK, the Tigerloop is two days old. Was it installed professionally? That professional should be there getting your system working. If you paid by credit card, call the credit card company and ask them to reverse the charges since you paid for a heater repair and the heater is still not repaired.
Now, to your problem.
Are you sure you have the Tigerloop installed properly? Is there a bypass plug installed in the fuel pump? You must have a bypass plug for the Tigerloop to operate properly.
Next, is the OSV installed properly? If the arrow is pointing in the wrong direction, you will have a problem.
The OSV should be installed after the filter, so there should be a filter between the tank and the OSV. If you get debris in the OSV, it will not work properly.
If you are getting foam, what color is the foam? Milky-colored foam is a sign of water in the fuel.
Direct the fuel into a glass or clear plastic container. Foam that contains only fuel will have a clear appearance. When the foam settles in the container, there should be no water in the fuel.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
this is not stuck, and there is no water in that fuel
You can ask the fuel tank installer to come out and drain the water from the bottom of your tank by removing the plug. Then ask them about this valve: McMaster-Carr 4921K84 It is rated for use with oil and would make draining water from the bottom of the tank easier and safer.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Foam is pink. It settles immediately back to red when it hits the bucket.
Oh no professional driving out to where i live without costing way more than i coukd afford. i installed it. i followed instructions and took the pump off, removed the return port plug, installed the bypass and connected the tigerloop to the return.
-I read the webster ovs shoukd be installed near the tank. My tank is exterior, 275 vertical tank, top drawl 4inches off bottom, near tank firomatic, webster osv, 40ft run, firomatic, tigerloop with filter. All are pointed in the correct direction. 3weeks ago after the cracked fitting and found water in the line, I reflared all connections and put new fittings on, tightened 26lbs with criwfoot torque.( last yr. I didnt know anybetter so i tighened them with a reg 3/4, guessing thats how i cracked the flare nut). after all that i Still had foam. Then 2 days ago, i put the tigerloop on. Still foam. Have you ever seen a cleancut pump be the cause of foam? If the 40ft run had foam, wouldn't it show up in the tigerloop? I have a hand pump siphon, could i drawl enough suction to test the line without the pump attached? That would tell me if its the pump or the line ir woukd i need a vaccum pump?
0 -
Does the top feed line from the outside tank have a fitting near the top where it curves to go back down to the ground? That fitting is a location for an air leak.
is the OSV and the Firomatic near the tank, outside, or is it inside the skirting of the home so it is protected from the weather?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
The bleeder on the fuel pump should not normally be needed once you have a Tigerloop installed and the system has been properly primed. During initial startup, you may need to open the bleeder to remove air from the pump and fuel lines. After that, the Tigerloop should handle the air removal automatically.
On your fuel pump, the bleeder port and the return port both provide a way for air to escape from the pump, although they serve different functions. You open the bleeder to let air out when you have a conventional one-pipe system. With a Tigerloop, the pump is configured for two-pipe operation, with the return line connected to the Tigerloop.
By leaving the bleeder closed, the air coming out of the pump travels through the return line to the Tigerloop. You will see that air in the clear portion of the Tigerloop, and the air will be vented automatically through the top of the Tigerloop.
If you are getting air continuously, then the 40-foot fuel line from the tank to the Tigerloop may have a leak that is allowing air to enter. It could be at the OSV, the Firomatic valve, or the dip tube that goes to the bottom of the tank. It could also be a bad flare fitting or a threaded pipe connection that does not have the proper sealant. Excessive vacuum or a restriction in the fuel line could also contribute to the problem.
Did you use Teflon tape on your fuel line connections? You should not use Teflon tape on fuel-oil piping. Manufacturers such as Suntec specifically warn against it, and its use may void the warranty on certain components. A small piece of Teflon tape can get stuck in the working parts of the OSV or fuel pump and cause the system to malfunction.
Find where the air is getting into the system, or what is causing the excessive air accumulation, and you will be much closer to solving your problem.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
I truly appreciate your help. Ive never been so frustrated and beaten down by something.
Yes, its a 4 tap bushing, copper tube attached with flare, i redid that fitting too. they are on the exteriir tank exposed to all elements. I had intentions of building a shed for the tank but im only one gitl and my to do list has gotten quite out of control. Its a 1yr old jacketed 3/8 line, so i dont think a leak is in the piping. Ill go through ur suggestions step by step in the am..kinda dark out there. Ill pay close attention to the bushing connection..maybe take the osv off and see if that makes a difference. ,
you know, i moved into this house in 2022, the tank was from the 70s with 1 line, no valves, no firomatics and i never had a problem..well until tbe rust fell off thebottom of the tank and ihad to tilt t5he tank to get me through the winter.
0 -
So now you have a new fuel tank and have paid someone to do that job.
I like to install top-feed fuel lines so that there is one continuous pipe running from the bottom of the inside of the tank, up and out through the tank bushing, and back down to the bottom of the fuel tank on the outside.
This creates a siphon that prevents air from leaking in through a fitting at the top of the tank. Once the fuel starts flowing, any leak in the fuel line will show up as a wet spot rather than an air leak that allows air into the high point and breaks the siphon.
Then a valve at the ground level with the OSV after the filter and all those fittings and parts are inside the building or skirting protected from the weather.
If you have several fittings that are connected near the top of the fuel line arc, that is a potential air leak that can cause the problem you are having.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
2 -
i doubt that a noticeable amount of water would get in a cracked fitting unless it was submerged so it is likely the water is in the tank. if the filter got water in it then it needs to be replaced. one or more of your flares could be bad. did you debur the tube? did you cut it square before you clamped it in the bar? did it crack when you screwed the cone in to it? did it slip in the bar as you drove the cone in?
1 -
-
Used a bit of 300grit paper, Deburred, wiped clean of particals, sanded. Checked for splits, compared against the fare head seal. Then torqued down. My flares are much better this year.
Shooot, i used a flare fitting in bushing. Should i switch to a compression?
The the OSV IT OPENS!!!!!!!!!! FUG…
0 -
It might be too late now but with the compression fitting Ed mentions or a regular compression fitting with the interion stop drilled out you can have a continuous copper line from tank to TL. As it is now you need to have tight fittings on the suction line in the tank and supply from the tank to the TL.
If you get a chance can you post pictures of you tank set up? we might notice something you've missed.
Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver
1 -
You on this forum have been so wonderful. I can't say thank you enough. Not once did u judge me for making due the best i could, everyone here straightup just offered help. Not many people like that in the world. Huge thank yous!!
Grallert, i see what your saying about the compression vs flare. Iwish id have known that last yr. Would have saved me ALOT of.. measuring..cutting.. oops i over cut.. so let me put a little union and tinee piece on the end. Loosening the compression to raise and lower the dip tube sounds heavenly.
So i think i got the foam resolved. Ever have a weird.. it just might work idea¿?? WelI i bled the line and RAN outside with my stethoscope to listen to the fittings while it was still under vaccum. I FOUND 1 fitting making thr faintest high pitched sound. I tightened it down with a regular 3/4 and the noise stopped. .u know, i retorqued each fitting to spec no less than 20xs
After tightening that fitting i
- Bled the line, foam mostly gone,, some light bubble pockets. Furnace wont fire. ( still no bubbles in tigerloop but intermintent bubbles in bleed line)
- Decided to check the pump gasket and strainer. Found rust inside., cleaned it up. Strainer had a few debris particles. Gasket is shot , waiting for new 1on 18th.
Yesterday i took out the gun assembly, the right electrode had a bunch of carbon. I cleaned em up and buffed with emery board.
Can i ask, id like to replace the nozzle and check the psi. is there a cheap gauge at harborfreight that will work.. i saw some online are over $100. I cant. I dont have that. My dog just.nevernind Its been a bad month.
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 135 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.2K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements