Pressuretrol with DO NOT ALTER sticker
Hello, I'm working on optimizing a ~15 year old steam system and the pressuretrol has a warning "The main scaleplate has an installed SAFETY STOP. DO NOT ALTER."
Based on what I understand though it is set too high and should be dropped down to Main 1.5 PSI and Diff 1 PSI.
Is this just a manufacturer deterrence sticker? Are my PSI settings correct?
Comments
-
The safety stop is that blank screwhead at the top of the main scale. It prevents the pressure from being set higher than 10 psig. That's way too high for your system anyway. The warning is to prevent someone from removing the stop and setting it even higher.
That is a subtractive pressuretrol, so the main scale sets the cutout (maximum) pressure and the differential controls the cutin.If this is a standard low pressure steam heating system, the cutout should be no higher than 2 psig and closer to 1.5 if possible, with the differential at 1. These controls are often not well calibrated though, so you may have to experiment. Unfortunately, the 0 to 30 psi gauge required by code is not usually accurate at these low pressures.
—
Bburd0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 134 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 52 Job Opportunities
- 18 Recall Announcements