Rinnai RE140e won’t stay running
Home built 2.5 yrs ago in warm weather climate. It is our second home. We’ve stayed there approx 10-12 weeks since the home was built. So, although the Rinnai is 2.5 yrs old, it has very few hours on it (this may be good or bad). I know I could have checked the actual runtime but didn’t think to do that when I had the cover off.
I arrived at the house yesterday and have no hot water. We don’t turn the gas off while we’re away. Actually I have a little hot water. I’ve been running the faucets or shower and will get a surge or HW, but it lasts less than a minute and then will run cold. If I turn tbe faucet off, wait a minute or so, it will start cold, then get hot, then cold again. This doesn’t happen every time. At one point with the faucet running the Rinnai ran for a good 10 minutes, but when I put the shower on (I left the faucet running also) it went cold within 30 seconds.
Pulled the cover and checked for error codes. The last 4 were: 12, 12, 11, 11. There were no other codes. Removed the flame sensors and igniter and cleaned them (they had very little carbon build up, likely due to low run hours, so I was not optimistic this would solve the problem). It did not.
What else should I be looking at? I thought tomorrow I’d pull the burner assembly and blow it out with compressed air. Check the fan motor for bugs etc. Look for any other obstructions etc (I didn’t see anything obvious today).
Any other ideas?
Took the unit apart this morning. It looks practically brand new inside. Blew it out with compressed air, but knew I was wasting my time. No change in performance.
intake and flue for blockages, sags that could or are holding condensate. it seems most likely something related to it sitting unused for so long since it has barely ran at all.
Exhaust is definitely clear since I had the unit running for 10 minutes or so at one point. Not sure where the intake is - but I checked everything I could and see no signs of debris or moisture anywhere. Since it will run for a brief period and then go cold, my feeling is it is having trouble keeping the flame. I ordered new flame rods. Although the ones installed look brand new I’ll swap them out when the new ones arrive. Other than that I’m not sure where to look? Control board?
it is an outdoor unit, so when it is running or trying to run do you smell gas at the exhaust? If not then either the gas valve isn’t opening or the manifold solenoids are not opening. A manometer would be handy to see if the gas pressure is dropping or not
Not great that I don’t have a manometer. If it’s the manifold solenoid(s) is there one or multiple? Is it more likely that the solenoid(s) failed (all for them?) or a control board problem? Do you know how the control logic works - what are the solenoids looking for to open? Gas pressure (is there a switch?), and a signal from the controller? Anything else?
is it actually calling for heat when it isn't firing? is the flow sensor sticking from lack of use?
I was away for a couple of days and got home early this morning and I’m back at it. I have some additional information…
I ran the sink tap. Unit runs, produces HW for as long as I can impatiently stand there at the sink or at the unit watching it run.I turned on the shower in the master bath. Error code 12 by the time I got outside.
Sink back on. Hot water again.
Tried the shower in bathroom #2 (reason why in a minute). Shower was hot. When I checked the unit it seemed to be putting out a lot more heat (at the flue) like it had ramped up and was running at a higher rate.
Turned the shower off and tried the master bathroom shower. Error 12.
Sink again = HW. Spare bathroom shower - this time error 12. So, inconsistent performance when running spare bathroom shower.
The only difference between the two showers is the flow rate. I removed the energy star water saver that restricts the flow from the master shower, so it has much higher water pressure and a higher flow rate (requiring more heat, of course). Note that this was done over a year ago (and 50+ hot showers since).
So…. I’m thinking the unit has some type of variable control (or multistage) performance and when it ramps up it’s throwing the error code.
Where does this lead me? Power supply? Gas valve? Control board?
check the gas pressure. may be inadequate gas supply because of a bad regulator or regulator with a clogged vent or an empty tank if it is propane. how do other appliances perform? if you have a gas range do the surface burners get smaller when it fires?
could be restricted airflow through the appliance too. it modulates by varying the inducer fan speed, the gas valve just provides gas based on the vacuum produced by the fan. if it can't get full airflow through the appliance it cant fire at its highest rate.
what were the results of the combustion analysis when it was installed? if the combustion os off it might fire at low fire and go out at higher fire.
Thanks for the response and comments.
Supply is nat gas. This is our second home (in FL) and I’m down here on my own. I’m not cooking much but I’ve had the stove on (1 burner) and haven’t noticed anything abnormal but I’m not using much gas. Being on my own also makes troubleshooting a challenge. I don’t have combustion results from the install, but nothing has changed. When I’m running the shower it’s the only thing on using gas in the house. I’ve opened the unit and it is pristine inside. When I was in there a couple of days ago I didn’t see an easy way to check to see if anything could have made its way into the inducer. It would have to have made its way into one of the slots on the lower side of the enclosure and then found its way into the inducer.
I have a plumber coming tomorrow who said the process is to link to Rinnai tech support via a video link and they’ll observe its operation and advise. If parts are needed they’d be sent by Rinnai, so no fix for several days. I’m driving from FL back to NY on Monday which makes this whole thing a royal PITA.
I’ll report back tomorrow after the tech support session.
is there a filter on the intake air? A slide out near the top?
Also a filter on the cold water side
These are the common maintenance items
Living the hydronic dream0 -
Inlet water filter is a great suggestion. The water here in FL is gritty and leaves a white residue on everything. It makes perfect sense. I’m gonna pull the filter and see what I find. I have a high degree of confidence this is it.
My initial excitement was met with immediate despair.
Pulled the inlet water filter. It was mucked up and definitely needed a good cleaning. Reinstalled it. No change in behavior. Hot water when I run the sink. When I turn the shower on it (and the sink) go cold. The unit shuts off and throws code 12.
Service Tech told me he was going to come by multiple times today but was ultimately a no-show. This afternoon I pulled the fan and it, like everything else I’ve seen, was absolutely pristine. Another cold shower.
if it is restricted before the gas valve, that could cause the symptoms you are seeing. restricted after the gas valve would just lower the firing rate. the first steps really are to look at the combustion and the gas pressure.
Hi, Following on @mattmia2 's thinking, this gas pressure test gauge would be a nice tool to have. I just used this to troubleshoot a problem job and found it quite helpful.
https://www.ebay.com/itm/307189635383
Yours, Larry
1 -
Are you thinking that gas pressure would be low due to an issue internal to the unit? What would that be? A problem with the gas valve?
The reason why I didn’t think it was a gas pressure issue is that the unit is located approx 2 feet from the gas main.0 -
i'm thinking either the combustion is misadjusted and it is going out when it tries to go to high fire or the gas pressure is dropping under demand, probably because of a problem with the service regulator or meter but it could be a problem in the street or a restriction somewhere too. there could be a problem with the gas valve too which is really just a regulator with a shutoff valve
Often troubleshooting is a process of elimination. Have you gone down the list of items the manufacture expects you to check with error codes 11 and 12 ? Checking off things that were absolutely verified ?
Since it once worked what has changed ?
Are the parameters the same as they were originally set and correct for the install ?
I'd review the Performance Data Table just to see if there is anything odd there.
Since it seems to be a flame issue.
Warranty ?
Personally, I like verifying the power supply first. And yes in this case that would include the gas supply.
Since if the power (or gas) supply is not working correctly how can you expect anything else to work correctly. However with equipment like this it is often hard to verify the power supply, substitution is often the go to method.
One Pipe System0 -
You've taken this thing apart pretty well, and from the pictures I can see, it's basically pristine. Given that this is an outdoor installation, there's no venting to be worried about; if there was a blockage, the unit would be throwing code 10 for a flue blockage. How long is the gas line going to the unit, and what size is it? If you're getting repeated 11/12 error codes, that is almost definitely a gas supply issue. Specs for NG are 4.0"-10.5" WC, with roughly a 0.5" WC drop when the unit fires. Get a digital manometer, check your incoming pressure at the inlet plug underneath the unit (highlighted below) while the unit is idle, then put a call to it and watch what happens.
1 -
Update and Recap
First, let me say thank you for all the comments and suggestions. Much appreciated.Quick recap of the situation: home is in FL Built less than 3 yrs ago in a large development (500 homes). We purchased to have a place close to our daughter. We are rarely there (total of about 10 weeks since purchase). There have been no changes to the system, no maintenance and no work of any kind done on the unit or the entire HW system prior to the issue with the exception of the removal of a flow restrictor in one shower head 2 years ago.
Unit has 480 hrs of runtime. Looks totally pristine on the inside: SS is shiny, no dirt, debris, spider webs, rust…. nothing. Flame rods, igniter etc look brand new - no carbon buildup whatsoever.
I can run the HW tap every time and get HW. If I run the unrestricted shower I immediately get code 12 and both the shower and sink are cold. Once I ran the restricted shower and the unit ran and went to high fire (up to that point I did not realize it even did that). This happened once and could NOT be replicated, but it definitely DID happen.
I’ve cleaned the flame rods and igniter with a dollar bill (even though it was obvious it wasn’t needed), cleaned the water filter (which definitely WAS needed - FL has crappy water that leaves white calcium? deposits everywhere), removed the burner plate (?) and blew it with compressed air, and removed/inspected the fan (which looked brand new on the inside).
As someone said above my approach to troubleshooting is to typically think about “what has changed” and in this case the answer is “nothing”, which makes me think it’s not anything “installation” related It worked fine when I was at the house 3 months ago, now it doesn’t Every house in the development has the same Rinnai unit (I asked when we purchased the home and was told there were zero options to select an alternative since it was approved as part of their Star Certification process) and I spoke with the guy who owns the house 50 ft from mine and his HW is fine so difficult to believe my gas pressure is the issue. The Rinnai hangs on the wall 6” from the electrical disconnect and maybe 3 ft from the gas main. It’s pipes with what I believe is 1/2” black iron (diameter looks like 3/4” copper pipe). Nothing is running in the house (I’m there alone, not cooking, and have the HVAC unit off).
I will p/u a manometer for future use, and part of this exercise for me is to get HW but also to get an education and learn about the unit to ensure I maintain it properly and that I can fix it when needed (thanks to all of you for that). I know the unit needs to be flushed occasionally and have that on my “to do” list for the near future, but it hasn’t been done yet due to the low run hours. I went out the night before I left (it was very dark) and didn’t see a regulator, but it makes sense to me that there would be one downstream of the meter.
Likely culprits (IMHO) are the 24v power supply, a gas valve issue, or a control board issue.
Unfortunately the service tech strung me along all day Sat and Sunday, and I needed to return to NY Monday morning. I’m mulling over whether to give him another shot, call someone else, or wait until I can drive back down (maybe first week of Dec). If I call a tech now my daughter would have to go over there and I lose the oppty to watch and learn.
Thanks again to everyone. Happy to hear other ideas but I’m unable to do anything while I’m 1000 miles away.
I think if you are cutting out with flame failure only when it goes to high fire and never for lower flow I would be investigating the fuel supply, and if what you say is accurate
"There have been no changes to the system, no maintenance and no work of any kind done on the unit or the entire HW system prior to the issue "
Then I would be most suspect of the regulator. The machine looks brand new
Logic dictates something changed, no mater how subtle, otherwise it would still work.
Maybe a loose piece of pipe sealing tape moved and is now restricting the gas flow.
One Pipe System0 -
How far from the main gas regulator is the unit? If you're seeing the code 12 as soon as the unit tries to kick into high fire, you have a supply issue. The 1/2" line will be able to supply enough gas to the unit in a low-fire situation, but when the unit needs to ramp up and use additional gas, 1/2" won't be able to supply the requisite fuel and the unit will snuff itself, hence the code 12.
did you check the intake air filter? Usually in the upper right hand corner ?
It can cause symptoms like a bad gas valve or gas pressure . Filters are one of the most common issue with tankless
there are you tube videos on troubleshooting and servicing that unit
Living the hydronic dream1 -
Thanks again for the comments. In response:
- there is no air filter. It is an externally mounted unit.
- I don’t agree the gas line is undersized. They’re building 500 homes. My entire neighborhood has the same unit, installed the same way. It worked as is for 2+ years piped the way it is. It’s possible the gas line could have some type of contaminant in it, but it’s not an issue where the line is undersized.
- the unit is mounted 30-36” from the gas main. The supply comes out of the ground and into the meter. From the meter is a single 1/2” (maybe 3/4”) line running parallel to the ground until it’s under the Rinnai. There’s a “T” directly under the unit. One side of the T runs up to the Rinnai; the other side continues parallel to the ground for maybe 18-24”, there’s a 90, and then it enters the house. I don’t remember if it’s a T or if it’s a cross with a drip leg, but there’s very little piping and it’s very straight forward.
- lastly, your are 100% correct that SOMETHING has changed. It would have been more accurate to say that “Neither I nor anyone else have made any changes to the system”. Nothing added, removed, adjusted or replaced. No one’s been inside the box until I had no HW.0 -
1/2" pipe is not even mentioned in the chart in the manual, I'd verify what it actually is. Also gas pipes can fill with water so even if it is 3/4" if it has significant water in it, it no longer functions as 3/4" pipe as far as the Gas flow is concerned. Which is why the pressure at the unit should be measured. Guessing its actual status is a poor way of troubleshooting.
One Pipe System0 -
I believe the OP mentioned they were getting a manometer so they could measure properly. It doesn't sound like they want to just guess at random
Thanks. My plan is to get a manometer or to have a service tech come and measure the gas pressure with one.
I’m not 100% sure the size of the gas line because I didn’t, and still don’t, believe the line would be sized incorrectly, so I didn’t focus on it. The unit’s run fine for 2.5 yrs. Every home in my development is done the same way. It went to high fire and ran one time while I was troubleshooting. The Rinnai is literally 2-3 ft from the gas meter. If the pipe was sized too small I would have had issues before this, and my whole neighborhood would be screaming about issues. I’m no longer at the house so I’m relying on my memory of what the pipe looked like. It is gray painted heavy gauge steel, APPROXIMATELY the size of a 3/4” copper pipe. It could be 1/2”. It could be 3/4”. I trust the piping company that landed the contract to pipe 500 homes knew what they were doing. Maybe I’ll be proven wrong, but I’ll be shocked if ultimately the issue is that the originally installed pipe diameter is too small.
@Slowhand63 Have you checked and rechecked the DIP switch settings in the unit? Inadvertently rubbing up against a DIP switch can happen.
Is the unit set up and selected to run on the proper type of gas?
This Rinnai unit exhausts directly outside, with a built-in top draft hood; is that correct?
After all you have done, it might be time to call Rinnai tech support. 1-800-621-9419.
Better yet, have the tech call while you are there to go through this issue.
All I am saying is you may be the first in the area to experience the issue, maybe it is the correct size pipe maybe not, contractors screw things up every day and if the pipe is filling with water… Maybe due to inactivity water has settled in your pipe.
One Pipe System0 -
At this point, you absolutely need someone with a manometer on-site watching what your pressures do. Are there any other significant gas fired appliances on the line? Everything is pointing to a gas supply issue, and for whatever reason, it's appearing now.
As long as gas pressure is good and the drop isn’t so great, we will find out soon… the problem here is going to be manifold solenoid or multiple solenoids not opening. It seems to run in a lower flow, but when called upon for higher flow it codes out. Now the solenoids (3) are attached to the manifold and can only be replaced by replacing the entire manifold. The unit may be under warranty but honestly is the free warranty part worthy of the expense of a service tech charge for 2 visits one to diagnose and another to replace the free part. Probably not.
update:
As I’ve explained, the house and Rinnai are in Florida and I’m back in NY. Had an appt yesterday with the same service co that ghosted me twice when I was at the property.
Appt was for 11am. My daughter went over to assist. Tech showed up at 2:58pm. They called me and I explained the issue (again!). Tech took off the cover, had daughter run the unit to demonstrate, then put the cover back on. Told her it was likely one of the four solenoids but since it was a warranty issue he needed a multimeter to test which one and didn’t have his meter with him (?). He left and said he’d be back next week. Daughter called and I told her I have a fluke in the garage but he had already left.
Thanks for the response hilltown. You may be onto something.
Tech also tried to tack on a $200 diagnostic fee but that’s a separate issue and this is a tech forum.
Parts and labor are supposed to be covered under warranty except for the $89 service visit. We will see. Extremely frustrating that the unit is practically brand new and has only 480 hrs on it. A brand new unit at Lowe’s is $795.
Unprepared for class, you get an F for the day. Diagnostic fee should be challenged. Not having a meter is very lame these days.
Sadly situations like this is why I repair my own stuff, I do the research and buy the tools and parts, when the job is done I keep what I bought and learned for next time. It usually just work out better for me.
" practically brand new and has only 480 hrs on it " I'd wait until its repaired before I point fingers.
Maybe find another service company that can actually do the warranty work when they show up.
One Pipe System1 -
Did the tech show up with the manometer that has been discussed at length? Looking for 4 numbers. if the tech showed up with no meter, and no manometer for a flame loss problem then you are really dealing with completely unqualified techs that are just taking you for a ride. You can't run service on appliances like this without a meter and manometer in your vehicle.
I don’t know if he had a manometer on the truck or not. I recapped what I know above. Other than a screwdriver to remove the cover I don’t think he brought any tools to the unit. Again, I’m in NY and the unit is in FL, so I’m a bit challenged to manage the situation from 1000 miles away. From speaking with my daughter it sounded like he had little to no intention of doing anything. I had previously described the issue multiple times. He asked that my daughter demonstrate the issue - she did, and he said he didn’t have what he needed. If he actually planned to repair the unit you’d think he’d arrive with a manometer and a multimeter (at a minimum).
The service company I called was selected from the Rinnai website and was the only one within 60 miles of my house. Perhaps on Monday I’ll start looking for someone else.0 -
Name and shame, that's embarrassing. Rinnai requires techs to complete trainings to get listed as an authorized dealer/service provider on their website, so that should be addressed.
- 136 Chimneys & Flues
- 16.2K Strictly Steam
- 52 Industry Classes