Trying to do some research for a family member (non tech savvy), who needs a modulating condensing boiler setup. I'm new to the mod-con arena, so just trying to hear some advice from on the ground with installers and longevity. I've mostly dealt with cast-iron boilers.

I know the install is very important regardless of make. Aside from that, what is your current recommendation for a modern mod con boiler? It seems the stainless heat exchangers are a must. I'm hearing about Weil McClain Evergreen Pro line after they supposedly worked the bugs out (stainless fire tube heat exchanger); Lochinvar Knight XL (stainless water tube) many swear by this design on this model even though its a water tube; Rinnai; Viessman and others.

This would be connected to a large radiator system. I know the water quality is of high importance with these models and annual maintenance. Is one manufacturer/ model/ design inherently better with cast iron radiators? Easier with part sourcing when things gone wrong? Are some more sensitive to magnetite that others? The new system would have a dirt Separator w/ magnet and a balancing valve among others. I've explained that the return water temp on these mod cons needs to be less than ~130/125 to get the most efficiencies from what I've gathered and that may introduce some contradictions with cast iron radiators. The homeowner is confident his home is over-radiated, so he understands it would not be running at 180 to get the most bang for the buck…. or so it seems like a new mod-con boiler(s) would only be more efficient on the milder winter days (fall/spring) but not on the coldest day(s) of winter.

The family member has gotten quotes with both WM Evergreen Pro or Lochinvar, possibly in a cascaded setup giving some redundancy. All things equal with install, what mod-cons do you think are made the best? Last the longest? Easier for the installer/ maintenance?

Are there other models they should be considering?

Thanks for your help

Comments

  • hot_rod
    hot_rod Posts: 28,593

    So many good choices. Most brands offer a basic model and a version with more features. I like the Lochinvar Knight. 20 year record of use now. I use most of the control features, so it is worth the exrea $$.

    Even if it runs 180, it will be more efficient because it modulates and should all but eliminate short cycles. On a zoned system, especially with micro zones the modulation is a big deal.

    It's the short cycling on CI boilers that drives efficiency numbers down.

    With ODR you should modulate down below 180 for most of the heating season.

    Do a radiator or fin tube count to see what BTUs are being delivered. Then a load calc would show % of the season at lower SWT.

    Idronics 25 has ideas for lowering swt.

    If you want to take it a step further download the past temperature data for the location. Put it into a bar graph.

    Screenshot 2026-10-28 at 8.31.22 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    rhasody
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,243

    Lochinvar is good, also Viessmann is good but $$$$ and their are others. Not sure about Weil McLain.

    Some like HTP and Rinnai.

    just stay away from Navien.

    I would probably pick Lochinvar

    rhasody