Uponor A2700A SS Manifold body end cap question
Has anyone here here removed and re-installed the factory end plugs on an Uponor A2700 series stainless steel manifold?
I am looking to install a differential pressure bypass valve in my system, and this is the best place to install it if at all possible. Trust me on that.
This is a 1" manifold body, with 1" ball valves. Measuring best I can, I'm guessing the plugs are an R25/1"BSPP thread with a flat washer or O-ring. The R32 fitting on the other end must be installed the same way. There is no information available from Uponor and I can't get a straight answer using a detailed AI prompt. I can't believe it's a press fit - if it was, it wouldn't need a nutted end.
Comments
-
on the Caleffi manifold the end caps have a gasket and are also assembled with Loctite. Basically a super glue type product
With two zone actuators you shouldn’t need a bypass valve. We suggest 4 or more zone valves, consider a pressure activated bypass. Maybe you are adding more actuators?
A better option would be a delta P circulator it will adjust its flow rate based on which loops are open. Also save 50-80% electric consumption
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The system has 3 manifolds, each with 5 loops of either 3/8 or 1/2 PEX. Homerun system with panel radiators. 1 Grundfos Alpha fir circulation running in constant pressure mode (mid setting). TRVs on emitters except for the two thermal actuators you are running on open panels. No PS pump. Westinghouse/HTP Universal fire tube boiler (no longer made). Set for 25F Delta T.
Concern is this: minimum flow rate spec for boiler is 1gpm. I've heard the flow meter for the Alpha is sketchy at best, but there's a lot of time where it's reading 0 gpm. My flow calculations show a really low flow system, and I believe it can be running under 1 gpm a lot of the time. I hear tea-kettling quite often. I'm not worried about dead heading the Alpha. But I figure a few more watts on the pump won't matter if I don't have to buy and re-plumb for a new boiler several years too soon!
BTW, was planning on installing a Caleffi diff bypass valve 😊
0 -
Try the Alpha in fixed speed 3.
The Alpha is a delta P circulator. You would have to lock it in fixed speed if you install a pressure bypass valve. So one or the other.
Can you attach a pic of the boiler piping. The boiler should be piped primary secondary or with a separator. That way it always gets the correct flow, if only one zone is open, for example.
Kettling sound could indicate inadequate flow through the boiler
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements