Viessmann Dekamatik HK1 blank screen

Options

How do I fix a Viessmann Dekamatik HK1 blank screen

Comments

  • 109A_5
    109A_5 Posts: 4,650

    Does it otherwise work correctly, or 100% dead ?

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,884

    Is the power on? Is it plugged in? Is there a loose cable from the control to the display?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • 109A_5
    109A_5 Posts: 4,650
    edited 1:43AM

    If 100% dead, check to see if the building power is getting to the unit. There are also fuses that can be checked if you can. When checking fuses, verify the building power has been turned off to the unit.

    image.png image.png

    Manuals found here.

    https://www.viessmann-us.com/en/services/downloads/historic.html

    Although I didn't find anything in the Troubleshooting section about a blank display.

    If the unit has good building power to it and all the fuses are good I would suspect the internal Low Voltage power supply has failed, disabling the display and all logic and electronics.

    If the unit works OK and just the display is blank, the display or the electronics that controls the display has probably failed.

    Sadly in either case it maybe as simple as a failed solder joint.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System