IBC ramp speed selection ?
=================================================
Ramp speed for all touchscreen controllers
How fast the boiler tries to raise the water temperature flowing through the heat emitters. |
|---|
With a |
A |
You can |
Below is a table that shows ramp speed vs time.
Ramp Speed | °F per Minute | °F per Hour | °C per Minute | °C per Hour |
|---|---|---|---|---|
1 | 0.06 | 3.6 | 0.033 | 2 |
2 | 0.12 | 7.2 | 0.067 | 4 |
3 | 0.24 | 14.4 | 0.133 | 8 |
4 | 0.45 | 27 | 0.25 | 15 |
5 | 0.9 | 54 | 0.5 | 30 |
6 | 1.8 | 108 | 1 | 60 |
7 | 3.6 | 216 | 2 | 120 |
8 | 7.2 | 432 | 4 | 240 |
9 | 14.4 | 864 | 8 | 480 |
10 | 27 | 1620 | 15 | 900 |
==========================================
( VX-110 into a 2-pipe 12g buffer which then feeds an in-floor with 7 zones. )
In this mode, it appears to use whatever burner % it needs to hit the temp rise rate.
They recommend setting 1 for in-floor, but do I consider the effect of the buffer tank ?
Its not clear if the temp rise is across the boiler or between boiler input and buffer tank sensor. My boiler loop will be flowing faster than the in-floor loops by anywhere between 2 and 6 gpm.
Currently in building maintenance.
Comments
-
You want to use ODR with high mass systems. That helps with the flywheel effect, a lot.
With the buffer, and ODR, the ramp is not that critical.
It might take some trial and error.
I started my shop radiant today for the first time today. The ramp did slow down the start up somewhat. The 8 steps were spread out over 30 minutes.
Once it hit the top step it stayed at high fire for hours.
So it depends a little bit on how you run the system.
In a home I think you want to tweak various settings with a goal of near continuous operation. Comfort, efficiency and longer component life when you lessen or eliminate on/off cycles.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements