IBC ramp speed selection ?

Options

=================================================

Ramp speed for all touchscreen controllers

How fast the boiler tries to raise the water temperature flowing through the heat emitters.

With a
fin tube baseboard radiator, you may want the water temperature to rise
quickly to provide heat as quickly as possible. This type of heat
emitter has very little mass, so it can heat up quickly. When the call
for heat is removed, it cools down quickly. Generally this requires a
higher (faster) ramp speed.

A
radiant floor, on the other hand, has significant mass, and therefore
takes a long time to heat up. When the call for heat is removed, the
floor is still warm and continues to add heat to the space for a
significant period of time. If the indoor temperature overshoots the
desired indoor temperature, we recommend reducing the Ramp Speed value.
Generally this requires a lower (slower) ramp speed.

You can
manually set the Ramp Speed by choosing a value from 1 to 10. A setting
of 1 will raise the water temperature very slowly and 10 will raise the
water temperature very quickly.

Below is a table that shows ramp speed vs time.

Ramp Speed

°F per Minute

°F per Hour

°C per Minute

°C per Hour

1

0.06

3.6

0.033

2

2

0.12

7.2

0.067

4

3

0.24

14.4

0.133

8

4

0.45

27

0.25

15

5

0.9

54

0.5

30

6

1.8

108

1

60

7

3.6

216

2

120

8

7.2

432

4

240

9

14.4

864

8

480

10

27

1620

15

900

==========================================

( VX-110 into a 2-pipe 12g buffer which then feeds an in-floor with 7 zones. )

In this mode, it appears to use whatever burner % it needs to hit the temp rise rate.

They recommend setting 1 for in-floor, but do I consider the effect of the buffer tank ?

Its not clear if the temp rise is across the boiler or between boiler input and buffer tank sensor. My boiler loop will be flowing faster than the in-floor loops by anywhere between 2 and 6 gpm.

30+ yrs in telecom outside plant.
Currently in building maintenance.

Comments

  • hot_rod
    hot_rod Posts: 28,486

    You want to use ODR with high mass systems. That helps with the flywheel effect, a lot.

    With the buffer, and ODR, the ramp is not that critical.

    It might take some trial and error.

    I started my shop radiant today for the first time today. The ramp did slow down the start up somewhat. The 8 steps were spread out over 30 minutes.

    Once it hit the top step it stayed at high fire for hours.

    So it depends a little bit on how you run the system.

    In a home I think you want to tweak various settings with a goal of near continuous operation. Comfort, efficiency and longer component life when you lessen or eliminate on/off cycles.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream