HTP EFTC 140W combi questions
I have a htp eftc 140w that I picked up second hand, in my install right now I don't want to use the dhw side, does turning off the storage tank mode make it only fire when there is water flow?
It may, however I could not confirm that in the manual. Even if you can disable or minimize the internal storage tank mode or setings, you bought a combi, I believe it needs to be piped completely as a combi even if you only put a DHW spigot near the boiler. If you don't purge all the air out properly damage may occur. And since you do not intend on using the DHW function daily you may need to purge the DHW portion occasionally so air does not accumulate in the boiler.
One Pipe System0 -
There is usually a flow switch on the hot water side of the boiler. If no water flows to trigger that, it will stay in heat mode. If the HX tank isn’t filled and there is never a call for DHW on a flow, then it should stay in heat mode.
No harm in checking with HTP tech support.
Living the hydronic dream0 -
I'm planning to connect water to it just don't have plans to use it, I turned off the storage mode and that seems work.
If I have a 50 gallon electric water heater with my electric rate $0.13 a kilowatt and propane at $2.29 a gallon is it worth running the combi?
i would call it a lp instantaneous water heater in this calculator
Some of the mod con combis give you a choice of always hot, or fire on demand. Always hot cost a bit more fuel, but quicker hot water.
Using .13 kwh and 2.29 lp
Id go lp
@hot_rod is the $100 or so I'd save a year worth it for the extra cycling that puts on the boiler?
To me, it depends on how badly it is cycling. With a mod con a lot of electrical parts will be in that cycle, relays, gas valve, inducer motor, prove switches. They all have a life expectancy. And if they are populated on a printed circuit board, it can be an expensive repair.
Some of the mod cons have data logging on the control.
If so, watch it after a few cold months. Some tell you how many cycles and the duration.
If not collect the data by camping out next to the boiler, pen in hand.🙄
That boiler is light years ahead of a fixed output boiler that is over sized. At least you can get down to 15,000 btu/hr firing rate.
- 135 Chimneys & Flues
- 16.2K Strictly Steam
- 52 Industry Classes
