Noritz NRCB199DV: E54/E57 again. domestic expansion tank was on the hydronic loop for years.

Options

Photos are from last year, BEFORE the repairs described below. I know
that's not ideal. I'm back at the unit Wednesday and will post current
photos and pressure readings then. Posting now because I'd rather know
what to look for before I'm standing there.

SYSTEM

  • Noritz NRCB199DV, manufactured Oct 2018. Space heating only - the DHW
    ports are capped, domestic hot water comes from a separate gas tank.
  • Rating plate: heating capacity 120,000 Btu/h.
  • Supply setpoint 160-165F.
  • Four zones on an Argo panel - zone valves, one circulator, plus the
    boiler's own internal pump.
    1. Basement baseboard
    2. 1st floor baseboard
    3. Owner's suite baseboard
    4. 2nd floor apartment, forced hot air through a 12x15 water-to-air
      coil in an attic furnace
  • Boiler is in the basement. The attic coil is above the 2nd floor -
    call it three levels of rise.
  • Mix of old iron/galvanized and copper. Municipal water.
  • No record of the heating side ever being flushed, cleaned or treated.
    No real maintenance for many years.

THE FAULT
Intermittent shutdowns on Error 54 (low heating water pressure) and
Error 57 (auto feeder open more than 600 seconds). Power cycling resets
the timer and it runs fine for a while, then does it again.

WHAT WAS FOUND AND DONE LAST YEAR
A plumber replaced the expansion tank and the boiler's internal
auto-feeder inlet valve. Two things from that job that I only recently
understood:

  1. The old feeder valve's internal black rubber filter screen had
    completely collapsed, squeezed down and turned INSIDE OUT.
  2. The invoice reads, word for word:
    "Replace expansion tank that's for domestic water with proper
    hydronic expansion tank #30. And proper pressure gauge. Pressure was
    low so turned up fill valve/prv to 15 psi. Boiler running at 20.
    That is correct to pressure."

So a DOMESTIC water expansion tank had been sitting on my hydronic loop,
along with a domestic 0-160 psi gauge (photo 4). Both were replaced with
an Amtrol #30 and a new gauge. Nothing on the invoice about setting the
tank pre-charge. The relief valve was not touched.

Less than a year later the E57 timeouts are back.

The expansion tank sits on the floor in the corner, several feet below
the boiler (photo 1, bottom centre). The new one went into the same
spot, just larger.

NO VISIBLE LEAK
Nothing wet, no puddles, no staining on the floor. The only thing I can
see is rust-brown streaking running down the side of the OLD tank in
photo 3.

PHOTOS

  1. Near-boiler piping. Argo panel on the left, old expansion tank on the
    floor at bottom centre.
    2. Same wall with the boiler's front cover off - taken by the plumber
    during that visit.
    3. The OLD expansion tank, the domestic one. Note the rust staining
    running down the shell.
    4. The OLD pressure gauge. Everpure, 0-160 psi.
    5. Zone valve manifold, on the wall opposite the boiler.
    6. Rating plate.
    7. Other side of the room - separate gas DHW tank, Argo panel, the
    circulator, and the old expansion tank on the floor at right. 1-Near-boiler piping. Argo panel on the left, old expansion tank on the%0A   floor at bottom centre.jpg
2-Same wall with the boiler's front cover off - taken by the plumber%0A   during that visit.jpg

3-The OLD expansion tank - the domestic one. Note the staining down%0A   the shell..jpg

4-The OLD pressure gauge. Everpure, 0-160 psi..jpg 5-Zone valve manifold, on the wall opposite the boiler..jpg 6-rating plate.jpg 7-Other side of the room - separate gas DHW tank, Argo panel, the%0A   circulator, and the old expansion tank on the floor at right.jpg

QUESTIONS

  1. What makes a feeder screen collapse and turn inside out? I assume
    flow went backwards through it. What drives that?
  2. If a domestic tank (40-ish psi pre-charge) was on a loop running
    15-20 psi, am I right that the diaphragm never moved and I effectively
    had NO expansion capacity for years? And would that have had the
    relief valve lifting and reseating every cycle - dumping water, the
    feeder making it up, over and over? If so, is the relief valve seat
    likely wrecked by now and weeping on its own, even with a correct tank
    fitted? It was never replaced.
  3. Is 15 psi cold fill enough with the attic coil three floors above the
    boiler? My arithmetic says that leaves the coil at roughly 2 psi,
    which sounds like air vents up there ingesting air rather than
    purging it.
  4. The tank is on the floor several feet below the boiler, and there's
    both an internal boiler pump and a separate circulator (photo 7). How
    do I confirm the tank is on the right side of the pump? If it's
    wrong, could the pump be pulling the top of the system toward zero
    every time it runs?
  5. Could years with no flushing in an iron system silt up the boiler's
    pressure sensor and give me a false E54 rather than an actual leak?
  6. A contractor has proposed capping the internal auto-feeder entirely
    and fitting a standard external fill valve with backflow preventer on
    the loop, to get past the 600-second timeout. Reasonable, or is that
    just hiding a leak I haven't found?

Tell me what to photograph and measure Wednesday and I'll get it.

Thanks.

Comments

  • hot_rod
    hot_rod Posts: 28,606

    water that is rusty like that could be an indication that the system is taking on fill water often. A leak in the system or the relief popping from wrong expansions tank pre charge

    Which could also mean the boiler is sludged

    Id run a hydronic cleaner through the system, Fernox is one brand

    You want 5 psi at the highest point

    .433 x the height to the AH, add psi

    The boiler needs to pipe primary secondary if it has an onboard pump, as combi do

    Nothing wring with a dhw expansion if it is charged properly

    The external fill valve, connected at the expansion tanks

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    fasterlight
  • Thank you - that's extremely helpful.

    Two follow-ups.

    On pre-charge: the new Amtrol #30 went in last year and the invoice says
    nothing about setting the charge. Factory pre-charge on those is 12 psi
    and the fill was set to 15. So I may have the same problem again with a
    different tank. I'll check the Schrader valve this week.

    On primary/secondary: this is the part I don't know how to assess. There's
    the boiler's onboard pump plus a separate circulator and four zone valves
    on an Argo panel. What should I photograph so you can tell whether it's
    piped primary/secondary or not? I'm at the unit Wednesday and I'd rather
    shoot the right things once.

    Also - the invoice from last year says the fill was set to 15 psi. I
    haven't verified that myself and I'll read it Wednesday. If the rise to
    the attic coil is roughly 30ft, 0.433 x 30 + 5 puts it nearer 18 psi, but
    I'll measure the actual height rather than guessing at both ends.

    One thing nobody has addressed: the old auto-feeder inlet valve's rubber
    filter screen was found collapsed and turned completely inside out. Does
    that tell you anything on its own?

  • hot_rod
    hot_rod Posts: 28,606
    edited October 6

    It is wise to put a pressure gauge on an expansion tank and confirm the pressure. Before you install it.

    A 12 psi, if in fact it was 12, with 15 fill pressure it will still accept some expansion as the water heats. The intention of an expansion tank is to "accept expansion" as the water or fluid is heated. While staying 5 psi or so below the relief valve setting. There are tables and formulas to calculate the "acceptance volume" based on fill pressure and pre-charge pressure.

    Amtrol actually uses 28 psi max. with a 30 psi relief valve in their calculator.

    In chilled water systems you can actually under charge the tank pre set allowing some initial fill water to enter the tank. So as the water cools, contracts, you still maintain some positive pressure.

    We do the same with solar thermal expansion tanks, allow a small amount of glycol into the tank so as system temperature drops in winter we don't go to gauge 0 psi.

    I don't know much about the onboard auto-fill, some Euro style fill valves have a rubber check to act as a backflow device. Maybe that failed.

    Ideally you want the fill valve connected the point of change. So pumps cannot change the pressure at that point.

    Yes it is possible to pull a negative pressure which could allow fill water to constantly enter when a pump runs, whick keeps the relief seeping and even more fill water.

    You have a valve on the expansion tank, drop the tank, add a tee and put the fill/BFD there.

    Screenshot 2026-10-05 at 8.06.58 PM.png Screenshot 2026-10-05 at 8.08.12 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    fasterlight
  • That lands. 54 is low pressure, 57 is the feeder open past 600 seconds -
    so they're two halves of one event rather than two separate faults.

    And the part I hadn't thought through: if the feeder runs a full ten
    minutes and the pressure still doesn't come up, the system isn't simply
    low on water. Ten minutes of fill would refill this loop several times
    over. So either it's leaving as fast as it arrives, or something is
    holding the pressure down at the sensing point while the feeder runs.

    Which leaves three, and they look distinguishable:

    • a leak, or the relief seeping -> decay test with the fill shut off
    • the pump pulling that point negative -> depends where the fill tees in
    • the feeder restricted again -> last year repeating, and a symptom
      either way

    Two questions:

    1. If I move the fill/BFD to a tee at the expansion tank, does that on
      its own rule out a leak, or should I still run the decay test first?
      I'd rather not fix one cause and assume it was the only one.
    2. Still hoping for the primary/secondary answer. Onboard pump plus a
      separate circulator and four zone valves on an Argo panel. What should
      I photograph Wednesday so you can tell? I only get one trip down there.

    Also - the invoice from last year says 15 psi cold, 20 psi hot. Against
    your 28 psi ceiling that sounds like the tank was accepting expansion
    properly at that point, which points away from the tank. I'll re-measure
    rather than trust a year-old number.

    Wednesday I'll post: where the fill valve tees in relative to the
    expansion tank, the relief valve discharge, and the near-boiler piping.

  • hot_rod
    hot_rod Posts: 28,606

    yes you certainly want to rule out a leak first off. That is fairly easy to do, with an overnight test.

    A bucket under the pressure relief valve tube tells if it seeps or discharges ocassionally. That is a cheap and easy fix if the valve is seeping

    It takes a few conditions to pull a negative pressure. Low fill, a high head circ and the placement of the circ in relation to the exp tank. It’s not common, but a possibility

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    fasterlight
  • fasterlight
    fasterlight Posts: 6
    edited October 11

    Update, and a sanity check on the plan before I hire someone.

    Correction first: the crystallization I mentioned is at the backflow
    preventer's vent discharge, not a relief valve. The heating relief
    discharge is dry.

    What I measured (NRCB199DV):

    • 7.5 psi cold. On power-up the feeder fills fast to 12, then
      crawls, and throws Error 57 at 600 s. It doesn't open at all
      from 10 or 12.5.
    • Expansion tank pre-charge is 12. Same knee whether I'm filling
      it or heating it from cold.
    • Still losing pressure: 12.5 after filling Wednesday, 10 cold
      Thursday, Error 57 on its own Friday morning. Floor is dry.
    • Feed line sits at 30 cold and climbs to 60 whenever the boiler
      fires. Water trapped between the BFD and the feeder solenoid.

    From the manual (Installer Mode I:14_HPS, default 12): fills below
    8, stops at 14. Going from 12 to 14 is only about 0.3 gal into an
    Amtrol #30, yet mine gained under half a psi past 12 before timing
    out. So flow through the feeder is choked. Noritz's Error 57
    procedure says check the inlet filter before replacing the feeder,
    and the feeder was replaced last year.

    Plan, per hot_rod and Noritz §9.1 / §18.1: drop the tank, put the
    fill and BFD on a tee there, pre-charge = fill = HPS (about 18 for
    the height, I'll measure), switch the internal feeder off
    (I:15_AFA) and cap it, and confirm the circulator pumps away from
    the tank.

    Separately, on the Argo AZ-6P one zone shows green but never red.
    The valve never proves open, so the boiler never fires for it.
    That's the cold room.

    Three questions:

    1. Anything you'd change in that plan?
    2. Any ideas where the water is going, with a floor that's been
      dry for two years?
    3. Does anyone cover northwest NJ (Randolph, Morris County)? I'd
      welcome a message.
  • My previous post was unnecessarily long, I updated for succinctness.

  • hot_rod
    hot_rod Posts: 28,606

    I think the zone valve light only comes on when the end switch closes. So either it is miswired, doesn’t have an end switch, or the end switch is bad?

    If you could set the system to 12 psi, let it set without firing for a few hours, does the pressure drop?

    Typically it would go to zero if you have a leak.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    fasterlight
  • fasterlight
    fasterlight Posts: 6
    edited October 11

    Turns out your test has been running since Friday: after a 57
    this boiler won't fire or feed until it's power-cycled, and nobody
    has touched it. It went from about 7.5 Friday morning to 5 now
    (remote camera, checked against a photo of the dial). Not zero,
    though the house has been unheated, so some of that may be
    cooling. Last time it sat at 7.5 for days.

    Could the leak be above the gauge, so it stops once the pressure
    up there hits atmospheric? 5 to 7.5 psi would put it roughly 12
    to 17 ft up. I'll keep watching it another day.

    On the zone valve, that matches the Argo manual and a local
    contractor, so I'll have the wiring and power head checked. He
    also recommends the fill at the tank under the air eliminator,
    pumping away, and an ECM circulator on the secondary.

    Last question, on the second-floor hydro-air zone (coil in the
    attic air handler, about three storeys up). The proposal was 180F
    for the baseboard zones, with a mixing valve and circulator
    taking the hydro-air down to 145F. Does that make sense for a
    hydro-air coil, or does it need the hotter water? Its supply pipe
    also only ever seems to get warm, never hot like the others. Not
    sure it was calling at the time, but if it was, would that point
    to low flow or air?

  • 109A_5
    109A_5 Posts: 4,687
    edited October 12

    It's late for me and I got a bit lost, so maybe my comprehension of the exact situation is a bit low.

    Anyway, kind of wondering if the boiler's electronics is incorrectly reporting the pressure (Error 54 (low heating water pressure)). So the need to add water is actually erroneous and the inability to fill is because the system pressure actually matches the pressure regulator setting. So nothing corrective is actually happening for 10 minutes, so then it locks out.

    Kind of explains why you have not found any leaks, and why the issue went away only to return some time later. Intermittent electrical / electronics do things like that, especially if things are moved around indiscriminately.

    image.png

    Do these gauge readings differ ?

    image.png

    Maybe get another pressure opinion here.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • hot_rod
    hot_rod Posts: 28,606

    As for the hydro coil question. The spec sheet will indicate the required supply temperature and gpm flow rate for the BTU output you need for the application. Also the air flow in CFM.

    The lower the supply temperature for all your emitters, the higher the efficiency of you mod con cooler.

    An example

    IMG_1659.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream