Sealing Chimney Liner Joints
I know that EK wants all liner joints sealed (I'm not sure how critical this is), and though the installer I'm speaking to doesn't normally do that it appears to be an option.
I see three joints: where the horizontal snout meets the vertical tee, where the tee meets the (20' 1-piece) flexible liner, and where the cap goes on the drop leg.
I was told that the tee that he uses is male at the top and inserts inside the liner: every tee I've seen had a female connector at top, which would seem to validate the need for a sealant. Are there tees that are male on top, and even if so, is sealant required?
I was also told that the drop-leg is only about 1 1/2" long and his intention is to leave the cleanout area below the tee sealed and we simply won't use it. If I'm correct, when cleaning the liner you would always disconnect the appliance and it's being suggested that one could vacuum out the tee and the drop leg through the snout: is this reasonable? Is it still reasonable if the drop-leg is 4-6" which they normally appear to be? If so, would one seal the cap in place?
If this is not the way to do it, I assume you'd need to extend the drop-leg down into the chamber and then cap it, and you'd have to remove/replace the silicone every time you get the liner cleaned?
Lastly, for the EK1, how far out from the wall should the horizontal snout come?
Sorry if I'm putting too much thought into this, and thanks for your help.
We do recommend sealing all of our joints as any air infiltration through joint leakage is less draft thru our boiler. Because we can get a brief time during ignition of positive pressure is an additional reason we ask for the joints to be sealed. The drop leg and tee connections at the bottom of the liner should be sealed also for the same reasons.
The flue connector from the boiler to the chimney should be 5 inch and kept as short as possible. We recommend less than 15 ft for this.
One final recommendation would be to confirm the front and rear door seals are tight in case there is any infiltration thru those seals.
Feel free to have the installer call here and ask for me if he has any questions.
Robert W.
Energy Kinetics
Thanks Robert, the EK1 would be directly under the tee so it's a short run.
Could you clarify what the 'front and rear door seals' refers to?
I'm also hoping there's a chimney sweep out there who can advise on whether sealing off the drop out and removing any soot via the tee is acceptable. It sounds like these run pretty clean.
Thanks again.
5 bolts in front and 5 in the back that have 9/16 nuts on them. One top dead center, one each side of burner, and two under burner. These match up in the back with same pattern. Just make sure they are good and snug.
Robert W.
Energy Kinetics
Noted, thanks.
- 135 Chimneys & Flues
- 16.2K Strictly Steam
- 52 Job Opportunities
