Old 1955 boiler 3 zone with 3 pumps 1/2 copper in basement floor radiant and the same in attic
Basment is 1 zone. Works good. 2nd zone. front part of home radiant 1/2 copper in attic over plaster i think could be drywall? Covered with vamiculike i thnk.and 3/4 plywood floor. 11/4 steel pipe drops and runs in basement in joists. 3 zone. Rear bedrooms same setup as zone 2. The prob is. When checking temps on 11/4 steel out and in pipes the pipe from boiler is very hot but the return is not very warm. All other returns are hot. OK I drained system installed antifreeze with a pump. Pumped it i to boiler drain and opened each zone bleeder above pumps to a bucket keeping below the coolant to get air out. Could I still have air in that back zone 3. When we did last time had to keep turning pump off pressure was going to high. I bought a smaller 1/12. Hp pump .was thinking fill 5 gal bucket with coolant pump into boiler drain.then put short hose from return from zone 3 bleeder and put it in bucket keeping it below coolant. And just let it run to see if I can force more coolant in. What should the pressure be on a cold boiler. If it helps may do all 3 zones
Pressure depends on the height from from the boiler to the highest point in the system.
Measure that height and divide it by 2.31. Take that answer and add 4 psi to it.
Most systems can run at 15psi for a two story house. You have to adjust the expansion tank pressure to match this.
Example:
25' from boiler to highest pipe.
25/2.31=10.8 psi
add 4psi= 10.8 +4=14.8 psi 15psi would be fine
If it was 35' high
35/2.31=15.15 +4=19.15 so 20 psi would be fine
Sitting off iys at 14psi
3 zones but how many loops? Is each zone only one 1/2" loop? Are there manifolds with multiple loops? Is there a mixing valve or two anywhere?
While pump purging, are you getting anything out of the return, or the pressure is rising too fast?
I've added antifreeze to systems with radiant, but in houses where there was also 5 fan coils and an indirect or 2, so I would isolate the radiant and fill the rest of the system with antifreeze. Then run all zones to check the level. In your situation, got a hand pump? There's snow melt glycol systems. Somebody here must know a trick to pump purge small radiant loops.
A good purge really comes down to valve locations. Can you isolate loops or zones and purge one at a time?
Some pics or a drawing of the near boiler piping would help us see your options.
In those old systems, it is a good idea to run a cleaner first, then install glycol.
Glycol only if absolutely necessary, it brings some baggage as far as pumping, heat exchange, leaks and cost.
Living the hydronic dream0 -
I was born in 1955, so I know all about those kind of systems.
You most likely have air in the loops that are not heating.
Let me see if I understand you correctly
What is working
- Zone 1 – Basement: Working properly.
- Zone 2 – Front of house: Appears to be working properly. The supply pipe from the boiler is very hot and the return is also hot.
- Zone 3 – Rear bedrooms: Problem area.
What is NOT working properly
Zone 3 has a very hot supply pipe coming from the boiler, but the return pipe is only slightly warm.
That suggests hot water is not circulating properly through Zone 3.
What you've already done
- Drained the system.
- Added antifreeze using a pump.
- Pumped antifreeze into the boiler drain.
- Opened the bleeders for each zone to remove air.
- Zone 3 may still have trapped air, especially because of the piping arrangement in the attic.
- You bought a smaller 1/12 HP pump to try purging the system again.
Your proposed plan
You are thinking of:
- Put antifreeze in a 5-gallon bucket.
- Pump it into the boiler drain.
- Open the Zone 3 return bleeder and run the discharge hose back into the bucket.
- Keep the hose below the antifreeze level.
- Let the pump circulate/purge Zone 3 for a while to see if more air comes out.
- If that works, possibly repeat the process on the other zones.
If I got that correct then there is one line in your statement that indicates that you have an air problem.
" When checking temps on 1-1/4 steel out and in pipes the pipe from boiler is very hot but the return is not very warm "
The 1-1/4" vertical pipe will not lend itself well to purging. You need to vent that zone at the high point.
The pump you use to force the antifreeze mixture into the 1-1/4" pipe is most likely connected to the system at the boiler drain with a 1/2" or 5/8" garden hose. If you somehow shut off the return pipe so that all of the boiler water and the water from your 5-gallon pail must travel through the 1-1/4" supply pipe and up to the top of the system, that part should work fine. There is a considerable amount of water in those pipes, but the flow should be adequate to push the water up to the system.
The problem occurs in the 1-1/4" return pipe.
The water flowing through that pipe will not be moving fast enough to entrain the air and carry it out through the purge station, which I assume is connected to the 5/8" or 1/2" hose returning to your 5-gallon pail.
If you are feeding the system through a garden hose at 2 feet per second, the velocity through the 1-1/4" pipe would be only about 0.32 feet per second, or roughly 4 inches per second.
At only 4 inches per second, I would expect a significant amount of air to remain trapped in the attic piping—particularly in those copper pipes buried beneath the vermiculite.
A 1/2 hp pump, even with washer hoses, will get you around 10 gpm. Thatis plenty for most residential 1-1/4 piped systems. A box store plastic sump pump would do it
Ed that all correct but I shut off the return under pump to boiler the blead in above pump. Should I shutoff the other 2 returns to boiler. Under there pumps. I added ball valves above and under all pumps so I could change them if they went bad without loss of antifreeze.
I'm not Ed, but yes. You're only purging one loop at at time so all valves should be off. You only open the drain valve on the loop you're purging. Obviously if there's a valve on the supply of the loop you're purging, it needs to be open.
What if I leave the return valve closed or just cracked open for a bit watching boiler pressure then slowly open to release to 5 gal of antifreese. By pump that's feeding the boiler drain.. 1/12 hp pump. Tryed a big pump but can't control pressure. By my self.kicked release valve mess.
Well the small 1/12hp pump worked great.have 15 gal drum of antifreeze mixed up. droped hose in ran to pump in drain in btm of boiler. then shutoff returns on all three pumps below them to boiler.abov e pumps are bib valves ran hose from 1 at a time to drumkeepon below fluid .started pump open valve on bib valves great flow .psi stayed about 15psi ran each zone for 30 min. Then on last zone shut bib valve off with pump on watching psi ran it up to 20 psi then shut all valves and removed pump. Using t/8 short hose all ran full stream.hope i got it fixed have not fired ot up yet. Also the 2 large valves? On top of boiler hot are old style flaper check valves .with a lever on side to force them to stay open.i find that's for draining system.or to use it with no pumps if needed. Thanks
- 135 Chimneys & Flues
- 16.2K Strictly Steam
- 52 Job Opportunities