Insulating Mains and Sizing Boilers
Spurred by the recent discussion on insulating steam lines I've been poking around seeing how much different amounts of insulation affect head load and sizing of the system. I've got the R value table from www.buyinsulationproductstore.com and I've been playing around with it.
A common setup I see in my area is a, normally 1 pipe, boiler in a 4 unit complex with a total of about 100 or so ft of main supply line that runs the perimeter and all the feed lines tee up and off of it. Some of them have no insulation, some do. Now if I put in a pretty common amount of radiation for this area of about 200,000btu I can see how insulating the mains affects the boiler load.
It seems to be pretty huge and definitely worth the cost to insulate your entire main. In this one example, without insulation, and 100ft of 3 in pipe the total load is 930 EDR. Now, if we insulate the main with 1" fiberglass at an R value of 5.2 we end up with an EDR of 812. That's enough to drop the size of the boiler down the next rating. Even 1/2" drops the load by 10%.
EDR Without Insulation
Radiator Calculations |
|
|---|---|
TOTAL RADIATION (BTU/HR) | 223277 |
TOTAL RADIATION (EDR) | 930 |
Radiator Output(EDR) | 800 |
Steam Main Output(EDR) | 126.3 |
Steam Upfeed Output(EDR) | 4.1 |
Column Radiators | 20 |
Tube Radiators | 0 |
Convectors | 0 |
Copper Cabinets | 0 |
EDR With Insulation 1/2"
Radiator Calculations |
|
|---|---|
TOTAL RADIATION (BTU/HR) | 196698 |
TOTAL RADIATION (EDR) | 820 |
Radiator Output(EDR) | 800 |
Steam Main Output(EDR) | 16 |
Steam Upfeed Output(EDR) | 4.1 |
Column Radiators | 20 |
Tube Radiators | 0 |
Convectors | 0 |
Copper Cabinets | 0 |
EDR With Insulation 1"
Radiator Calculations |
|
|---|---|
TOTAL RADIATION (BTU/HR) | 194888 |
TOTAL RADIATION (EDR) | 812 |
Radiator Output(EDR) | 800 |
Steam Main Output(EDR) | 8.0 |
Steam Upfeed Output(EDR) | 4.1 |
Column Radiators | 20 |
Tube Radiators | 0 |
Convectors | 0 |
Copper Cabinets | 0 |
Owner
Steamnowrockford.com
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 122 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements