hot water shop floor heat
I have a shop floor heat system. Wondering if my installation is ok . It is 4 runs of pex connected to single manifolds. The out water temperature is only about 80Degree Farhenhite to maintain room temperature at 58 degrees. Any changes I should do ?
Comments
-
-
Honestly, sounds like it's running great. 80° water might sound low if you're used to baseboard or radiators, but for a radiant shop slab maintaining 58°, that's pretty much spot on.
Since the slab has so much thermal mass, you only need the floor a few degrees warmer than the room air to hold temperature. Plus running water that cool keeps your fuel costs way down, especially if you're running a condensing boiler or heat pump where low return temps keep it in peak efficiency.
A few quick things worth checking just to be sure:
Check the temp difference between your supply and return manifolds. You want to see around a 10° to 15° drop across the loops. If return water is coming back way colder than that, your pump flow might be a bit slow.
Also make sure your PEX loops aren't over 300' each for 1/2" line, or friction starts killing your flow rate.
Lastly, what kind of heat source are you using? If it's a standard non-condensing cast iron boiler, make sure you have mixing/protection installed. Returning water that cool directly back to a cast iron block will cause flue gas condensation and rust it out over time.
If the shop stays comfortable at 58° on cold days and your loop lengths are balanced, I wouldn't mess with it much. Sounds like a solid setup.
Tom Gabison
National Boiler Supply — commercial boiler & hydronic parts
nationalboilersupply.comTom Gabison|National Boiler Supply
https://www.nationalboilersupply.com0 -
The picture looks like a wall hung electric boiler @Tom_at_NBS but I could be wrong.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
how many square feet is the shop?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Ah, I completely missed the picture on my end earlier! Good eye, you're dead on.
That's an Argo wall-hung electric boiler. No gas lines or exhaust venting to worry about, just that heavy electrical whip on the bottom left. That yellow sticker on the front boasting '100% Efficiency' is the dead giveaway for electric resistance. It's doing exactly what it's supposed to—just quietly feeding that 4-loop radiant manifold with the help of that little Grundfos circulator.
Tom Gabison
National Boiler Supply — commercial boiler & hydronic parts
https://www.nationalboilersupply.com]nationalboilersupply.comTom Gabison|National Boiler Supply
https://www.nationalboilersupply.com0 -
Still waiting on @mokomon to explain the problems they are encountering!
If there are no problems, and you are just asking what you should do about your existing set up… My advise is very clear.
"If it ain't broke, don't fix it"
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Thanks for the replys . I wasnt sure if the low output temperature was a problem for the boiler tank as far as rust . I am assuming that it is a closed system that corrosion shouldnt be an issue. Just a note … the shop is 1000 sq ft, 4 -250' runs of pex making it single zone. 18 deg differential between in and out temps.
0 -
no problem with low supply temperature.
With 80 SWT, 62 return , assumed flow of 2 gpm, (1/2 gpm per loop) you are delivering 18,000 btu/ hr to the space.The differential is just an indicator of the heat being delivered at that point in time. It may be wider on cold start and could tighten to 10 or less as the thermostat satisfies. Residential radiant designs around a 10-15 delta, for example.
Is 58 warm enough for working in the shop?
Was 58 on a cold day, or design day?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
0
-
58 is warm enough when i am working in the shop in the winter. Winters here only hit about 34 F, some times 28F
0
Categories
- All Categories
- 87.7K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 122 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 17 Recall Announcements