Out of 6 we installed between 1999 and 2001, this was the last one that was still in use up until yesterday. They were one of the only decent condensing boilers that were available back then.
We are replacing it with a Viessmann B1HE.

IMG_2088.jpeg IMG_2089.jpeg IMG_2091.jpeg IMG_2095.jpeg
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab
HVACNUTGGross

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,584

    25 years is a good run for a mod con I guess. Some CI boilers won't do that now.

  • hot_rod
    hot_rod Member Posts: 27,933

    Original expansion tank also?

    Did it develop a leak in the hx?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,816
    edited 1:16PM

    Yes, same tank. I never tested the charge. It seems like a benefit to have an on-board x-tank, but you have to drain the boiler to test the charge on the tank. Also, it’s a proprietary part and not something I carry on the truck.

    The boiler was still sound, but the owners are getting older and thought it was time to upgrade.

    Commissioning the Viessmann was all through the app. Even the gas type - this one is propane - is selected on the app. No mechanical adjustment on the gas valve.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
    GGrossmattmia2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,584

    @Alan (California Radiant) Forbes

    So, the owners are getting older and wanted it replaced but you are the same age you were when you installed the old boiler 26 years ago…….Right? LOL😊😊😊😊

    I keep thinking anything installed in the 80s is new equipment to me.

  • mattmia2
    mattmia2 Member Posts: 17,631

    the 70's was 30 years ago, right?

    GGross
  • GGross
    GGross Member Posts: 2,000
  • mattmia2
    mattmia2 Member Posts: 17,631

    but you can plug it and put another tank somewhere else…