How to properly Purge with caleffi Fill/Purge cart?
The instructions that came with the cart isn't the greatest.. you think for the price it would be a little better.
So how do you properly Purge a system with this? Obviously you put a valve in the system with the hose bibs on either side of the valve..
But do you fill the cart partially? If you have the feed valve open won't it flood the cart? I just want to know how to use this thing right any help would be great thank you guys.
Comments
-
It depends on how you have purge valve set up. Are you doing a zone by zone, or the whole system at once. You can buy purge valves, Webstone is one brand. Or build your own with a ball valve and two hose valves.
Get a Webstone, they have good purge cocks, better than a boiler drain for pumping into.
Shut off the fill valve
Fill the tank with about 10 gallons of water.
Pump into one valve, purge back into the tank from the other valve/ hose.
If there is a lot o0f air in the system you may need to top off the tank. As air comes out water from the tank replaces it.
You can also add a cleaner to the tank and circulate that for a day, if you have a dirty system.
This graphic shows pumping DI water into a system.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Pretty easy instructions to follow. even has pictures:
Looks like you need to add their three valve fitting to the piping somewhere
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
The pump cart is just a tool, there are many ways it can be used and connected.
Mostly they are for filling systems with glycol.
In some cases they get used to circulate a cleaner at high flow rates to scour a system.
Filling solar thermal systems.
Filling and flushing A2WHP loops.
Or purging problematic GEO loop fields.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements