Vitodens 100w b1ke-199 DHW temp not respected
I have a new Viessmann Vitodens 100w b1ke-199 combi-boiler (DHW + Heat supply for 2 hyrdonic air handlers). This is all < 1 year old.
Ever since we got it, the DHW hot water "scalding hot" (hurts your hand). I got around to setting up ViCare and set my DHW to 115F. When neither the DHW or Heat are being pulled, the ViCare app shows ~115 to 130F for DHW. However, when i start to draw hot water with EITHER DHW (ex. running bathroom faucet) or the heat supply - i can see in the app the temp fluxuates between ~ 115F and 140F, usually staying closer to top 140F range (which is that "too hot" temp).
In the ViCare app, i have a DHW schedule (5:30am - 10pm) and Operating mode switch (DHW) = Standard.
Any idea what could be causing this and how. i can adjust it? This seems like it should be a trivial setting.
Comments
-
First thing I would check is if there is a mixing valve under the unit? When these run hot in space heating they have no choice but to overtemp the DHW, a mixing valve is required in my region for all combi boilers for this reason.
next would be to check what the temp is actually coming out the faucet at. I dont use the vicare app much but the DHW matching exactly with the space heating temp is a little odd. is the DHW scalding you when it comes out of the faucet?
0 -
Have you called the person or company that installed it? Or did you install it yourself?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
yes it’s scalding coming out - I measured at 136F just now
I’ll check for a mixing valve but will have to look up one looks like.
0 -
0
-
GC has his sub o stall it. My GC it turns out is not good and doesn’t like to take accountability when he can avoid it - trying to self educate before going back to him
0 -
it will be a 3 way valve, likely with a plastic cap to make adjustments, and sometimes they have a temp gauge on the outlet (but not always) typically if the temp in the boiler from space heating were overheating the domestic it would cool off after a short while. if your system makes high temp water for space heating you would need a mixing valve (regardless of codes etc) if the system is all low temp (in floor heat) you may also have something wrong with a sensor in the boiler, though it does seem to be reading the temp correctly on your app.
0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 431 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements