Anybody happen to know any specifics on this vintage Dunham valve? Old enough that the distributor doesn't have any real info on it, and had no luck scraping the internet for info. We're thinking a a suitable replacement might just be a modern balancing valve but wanted to see if one of y'all might have any esoteric knowledge about it.

IMG_6593.jpeg IMG_6589.jpeg

Comments

  • hot_rod
    hot_rod Posts: 28,585

    I imagine it may be a simple butterfly valve inside that the lever moves to one of 3 positions.

    It looks like the lever is 180• off from normal. The screw locks the lever into the indents, I think.

    It may be a basic graphite string packing under the stem nut, if that is the leak problem. Maybe just try tightening that outer gland nut?

    I'm not sure you will find a valve to fit that flange to flange spacing?

    You might try Mepco, looks like they took over the Dunham product line. Someone there could identify the valve perhaps.

    https://www.mepcollc.com/product-literature/

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    pumpcontrolguy
  • Big Ed_4
    Big Ed_4 Posts: 3,584

    Its a flow check, it prevents the hot water from the boiler to rise up to the radiators once the heat circulator shuts off …

    There was an error rendering this rich post.

    GrallertpumpcontrolguyMad Dog_2mattmia2
  • @hot_rod @Big Ed_4

    Thanks guys,

    We work in more of a niche field of this sort of thing so It's not something we usually quote. But the customer is very bureaucratic and when they want something, there's no changing their mind, and they wanted new quoted.

    I wasn't actually the one on site to actually see it what the rest of the surrounding plumbing was. It was one of my other guys and they sent the photos to me to ask with what it was because

    I had checked with our Dunham/Mepco distributor and he said he wasn't familiar with it.

    I was originally thinking it was a old school triple duty valve, but yea after a closer look with your comments it looks like its just a check valve that you can also force open or closed, not throttling

  • Big Ed_4
    Big Ed_4 Posts: 3,584

    Open, is open . Closed is not a shut off . You can set it to Closed if Normal does not work .. The pipe off the top was connected to the expansion tank at one time ..

    There was an error rendering this rich post.

    pumpcontrolguy
  • hot_rod
    hot_rod Posts: 28,585

    Where is it located in the piping? Discharge of the pump?

    This is a similar valve in that it is a check, flow balance, and shut-off. Often called a triple duty valve.

    Typically found at the pump discharge. It may have the same flange to flange dimension.

    I would call Mepco to confirm it could be a swap out component.

    Screenshot 2026-02-20 at 2.48.34 PM.png Screenshot 2026-02-20 at 2.47.14 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Steamhead
    Steamhead Posts: 18,987

    @Big Ed_4 is right. It's a flo-check. Not sure what size it is, but it's definitely out of production. IIRC TACO makes one that can be installed horizontally as well as vertically. This might require changing the length of the pipes, but it will work.

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

  • JUGHNE
    JUGHNE Posts: 11,649

    B & G FAS flow control….2" X 2".

    I have some on a 1961 boiler. Might have the flange on one end only.

    There is a small lever on the top to put in permanent open mode.

    No "Off" position. Weighted lift check in side that pump pressure would open.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,236

    I agree it is just a standard flow check.

    The "flow control" name leads you to believe it is something exotic.

    I have seen one that looked similar the one above may have been made by Thrush.

    Why is the lever turned the wrong way?

    It should be set to open-closed or normal with the screw set in the divot.

    Triple duty valves, zone valves, control valves that are flanged are not so easy to replace. They are not like flanged globe or gate valves that have standard dimensions. They have whatever measurements the mfg decides on.

  • Thanks everyone,

    Very familiar with triple duties as I work more with large building systems rather than resi scale things, so usually HW pumps just have normal checks with drives, or triples duties with starters, or TDVs with bypass drives . Kinda seems like the flow check is usually more of a smaller scale solution than what I usually see.

    As, to why the handle is backwards, no idea. That's a better question for the site engineers and sometimes the things those guys do makes you wonder, 😂. Who knows if the entire system even works properly. This is the kind of building where they say "Quote this" and you quote exactly that no matter what is actually wrong.

    I wasn't on site there, only have a few photos from my guy that was there, so I have limited info to work with, but it's 2.5" pipe. B&G's used to make flow checks in that size but they're obsolete now unless I can find new old stock so it looks like I'll likely be tracking down a Watts 2000-M5 and we'll tweak the piping as needed.