Combustion question
Hey so today I went to an oil Furnace Service call and was getting a combustion reading at the end. I understand as long as CO levels are under 100ppm in the exhaust its fine, but I thought under 50 is ideal. What would cause these elevated levels? (See photo). I have -0.02" of draft over fire, pump pressure at 150 psi and had a .50 60B nozzle in there. It was a beckett AFG burner. L head if that means anything.
Yesterday I did a maintenance a year after the install. And I was called back today because they had no heat. It was on lockout. I check oil flow and it was good. I fired it up and it seemed to be rumbling and then the flame went out. Long story short I had to bring the Co2 from 11 to 12% and that made the difference. Can someone help me understand why choking off some oxygen stopped the rumbling?
Comments
-
What model furnace? I had one recently. New installation no heat on a Boyertown furnace, Beckett AFG with the L head.
Combustion test beautiful. 0 smoke.
It came back in the next day no heat. There's oil on the L head. I reset and it fires right up. Combustion test numbers are different. O2 and excess air went way up. I pulled the burner. Got the T-Gauge and checked the Z dimension. The assembly was 3/4" back from specs. I set the Z and dialed it in. Haven't heard a peep since. Check the Z dimension.
2 -
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 116 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements