Pulling a 'C' wire from a Honeywell R132A2K-2 relay box

Options
iwantheat
iwantheat Member Posts: 5

I have a multiple-zone oil-fired furnace using the Honeywell R132A zone relays. Some of these relays are controlled by old Honeywell T87F thermostats, while one is controlled by a bit more modern RobertShaw/Maple Chase 9600 digital thermostat. With both the T87's and the 9600 thermostats, the blue and red thermostat wires are connected together at each thermostat. I wish to replace all these thermostats with 'smart' thermostats which require a 'C' wire. Attached is a photo of the R132A with its cover removed. I also have access to the back-side of these units where the secondary terminals of the 24VAC transformer can be found. My thought is to separate the blue and red wires at each thermostat, and use the blue wires as my C-wire, removing it from B1-2 at the R132A and soldering it to the appropriate pin on the 24V transformer. But I am not quite confident as to the function of the B1-2 wire, and wonder if this procedure will cause me trouble.

F522A203-29E0-4CA2-B58C-A4CA33597209_1_105_c.jpeg
HVACNUT

Comments

  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,675
    edited February 16

    I’m sure there’s a way to find a “C” wire in there somewhere, but it may not be an easy connection.
    If you don’t mind spending some money for an easier way to wire the thermostat, get a Taco SR501 that gives you a “C” terminal. Taco or Caleffi also have them for multiple thermostats.
    You will need to make sure that the on board transformer is large enough to power the thermostat(s) whichever one you choose.
    My guess that the B1-2 and R2 terminals don’t go to your thermostat, rather they are dry contacts that turn on the boiler.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • 109A_5
    109A_5 Member Posts: 3,823

    It looks like there is no 'C' terminal as it is thought of now. However the non-switched (by the thermostat) side of the transformer is usually the 'C' wire functionality. However keep in mind that the relay was probably never designed to have additional loads connected do it. Adding additional loads may make the transformer fail due to mild overloading.

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,928
    edited February 16

    There is no terminal that equals R and C from the transformer. W1 is the only terminal directly connected to the transformer. If we call that R for thermostat purposes then the C is connected internally to the relay coil and there is no screw terminal does that particular node of the control (the Blue highlighted wire). The W for the thermostat purpose would be B1-2

    Screenshot 2026-02-15 at 7.41.03 PM.jpg

    This is an obsolete control technology from more than half a century ago known as Series 10, developed by Honeywell.

    A Series 10 thermostat uses a three-wire configuration: R, W, and B.

    In a Series 10 system:

    • When R and W close, the thermostat does not directly energize the burner or main control relay.
    • This initial contact establishes part of the control circuit but does not yet complete the relay coil circuit.
    • When B and W close (while R and W remain closed), the relay coil circuit is completed and the relay pulls in.

    This staged switching arrangement was intentionally designed to create a wider operating differential through the sequencing of contacts.

    Once the heating appliance begins delivering heat to the space, the room temperature can rise quickly. If the relay were allowed to drop out immediately upon slight temperature rise, short cycling could occur. To prevent this, the R–W connection remains closed, which holds the relay energized until the thermostat fully satisfies and opens the R–W connection at the end of the heat call.

    This “make-before-break” contact sequencing is characteristic of Series 10 controls and differs significantly from modern 24-volt control systems.

    I have a link to a Honeywell booklet that explains Series 10 controls in detail. http://www.hvac.amickracing.com/Controls/Heating%20Control%20Handbook-Honeywell.pdf

    But this will not help you with connecting a smart thermostat to this R132A control. There is no screw terminal anywhere on the control that will get you where you need to be. Your best bet is to replace that R132A with a Taco SR501 that has a dedicated C terminal for smart thermostats

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Alan (California Radiant) Forbes
  • 109A_5
    109A_5 Member Posts: 3,823
    edited February 16

    It could be modified (however there is still the transformer loading issue), screw terminal functions could be reassigned, but the Taco SR501 is probably the most practical solution.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Alan (California Radiant) Forbes
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,928

    That might work if the system does not have another series 10 device after that R132A that requires the use of the rest of the terminals. And even of you don't have other controls after that R132A, Do you really want to take the control apart and start redesigning the internal wiring with a soldering iron?

    I know that there are some that would do it, (including me) but you take that system into your own hands after a modification like that. If it happens to be discovered after an event that requires an insurance inspection you might be left holding the bag with cancelled coverage. (that is not something that happens very often if you are interested in saving $$$ by using the existing control.) Just a heads up!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • 109A_5
    109A_5 Member Posts: 3,823

    @EdTheHeaterMan Just presenting options, in general (for the average public) I think the Taco SR501 (or like) is probably the best option.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,928

    Agree @109A_5

    As I stated I might even try your idea given the opportunity. But not for a customer.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • iwantheat
    iwantheat Member Posts: 5

    Thanks, everyone. This is all great info. For multiple reasons (less money, less labor, etc), I would prefer to use the existing Series 10 equipment, rather than upgrading to a Taco unit. It's sort of an historic home, and I am fascinated by this old equipment. So here is what I am now thinking: Since it appears that my thermostat wiring is only 3-wire, and all conductors seem to be used in the current configuration, I need to free up a conductor for use as the C wire, and attach (solder) that conductor to the appropriate point at the 24VAC transformer.

    The current configuration has the R1 screw terminal attached to the red conductor, and the B1-2 screw terminal attached to the blue conductor. And the W1 screw terminal is attached to the white conductor. At the 9600 thermostat, the white conductor lands on the Rh terminal (which is also bridged ro Rc), and BOTH the red and blue conductors land on the W terminal.

    So since both red and blue conductors are tied together at the thermostat terminal, I figure that I could free up this blue wire (to use as a C wire) by disconnecting it from the red wire at the thermostat, unscrewing it from the B1-2 screw terminal in the Honeywell relay box, and then bridging the R1 to the B1-2 in the Honeywell box. After this step, I am pretty sure that electrically, nothing has really changed, and now I have a free (blue) wire that I can tie to the relay's 24VAC transformer and therefore use this blue wire as a C wire for the smart thermostat that I will install (replacing the 9600). Does this all make sense? Of course the extra loading on the 24VAC transformer might still be an issue, but I am willing to take that risk. (If it burns out, I can always go the Taco route! 😀)

    HVACNUT
  • It would be nice to get the whole picture. You have two wire bundles coming into the transformer relay. One to the thermostat and the other to your boiler. The one to the boiler might be daisy chained with other R132A's. Where do they land at the boiler?

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • HVACNUT
    HVACNUT Member Posts: 7,367

    What's the va rating on the transformer in the "historical" switching relay?

  • iwantheat
    iwantheat Member Posts: 5
    edited February 16

    Correct, I have not been focusing on that. I have found a junction box where all of the R2/W2/B1-2 connections from the various R132A's are tied together (each conductor color is assigned its own wire nut),

    FC59BBFA-F27E-4205-8315-864F292DC3E6_1_105_c.jpeg

    and then another thermostat wire that goes from this junction box to a splice (again with wire nuts) to another thermostat wire that goes to the burner unit.

    IMG_1386.jpeg 0E426931-08B4-4D09-B0B3-66CC172A2684_1_105_c.jpeg

    One thing I now notice is that these blue wires ultimately don't land anywhere unique, either, suggesting that I could probably just disconnect these wires from the B1-2 screw terminals in each of the R132A's.

  • 109A_5
    109A_5 Member Posts: 3,823

    " I have a multiple-zone oil-fired furnace using the Honeywell R132A zone relays. Some of these relays are controlled by old Honeywell T87F thermostats, while one is controlled by a bit more modern RobertShaw/Maple Chase 9600 digital thermostat. "

    As @Alan (California Radiant) Forbes stated the bigger picture would help.

    Where does the B2, R2, W2 wires go to ? It does not seem like that would go to another thermostat.

    It seems you have no series 10 thermostats. You mention multiple R132A zone relays. Is there any other zoning equipment, circulators or zone valves ?

    Freeing up the blue wire seems to be the least of the concerns I would have.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,928

    All of your controls on the boiler have been upgraded to series 80 controls as far as I can see. The old Series 10 stack relay RA117A primary control has been replaced with a Series 80 Protectorelay R8184G. You are using a 2 wire thermostat. What value is there in keeping the last of the Series 10 controls? The rounded black cover?

    If look on e-bay you may be able to find something that you can stuff under that black cover

    Screenshot 2026-02-16 at 1.55.47 PM.jpg

    Above are from 2 different e-bay listings.

    Or a better idea is to use an isolation relay with a separate transformer that has enough power to operate both the thermostat and the relay.

    Either way, you will need to buy something more that what you already have. Here is one isolation relay with transformer that was posted by someone else that I liked. I have modified it with your relay connected

    Screenshot 2026-02-16 at 2.04.04 PM.jpg

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • iwantheat
    iwantheat Member Posts: 5

    The B1-2/R2/W2 from the different R132As all get tied together and ultimately go to signal the burner to fire up. The red and white (line voltage) wires (entering the bottom conduit on the right hand side of the picture that I included in my original post) go to a circulator.

  • iwantheat
    iwantheat Member Posts: 5

    @HVACNUT I am not sure about the rating of the 24VAC transformer, but I think I might have read somewhere that it was 20VA.

  • 109A_5
    109A_5 Member Posts: 3,823
    edited February 16

    I guess if you want to go forward with your experiment I would modify the R132A this way, where the X - X are paralleled across the multiple R132A relay's to control the burner. Relabel the connections and document the changes so you or someone else can figure it out in the future without spending a lifetime there or just ripping it all out in frustration. And only one thermostat per R132A.

    At least where I live, I probably would not do this change this time of year in case things go badly.

    image.png