This boiler was installed this summer so not even a whole heating season yet it has very loud intake. We had the installer put in a Lochinvar intake silencer helped a bit. Probably not related but then it started leaking at the bottom of the condensate drain and has been replaced twice

See pics

IMG_4973.jpeg IMG_4974.jpeg

Comments

  • GGross
    GGross Posts: 2,104

    Can you take some pics showing the whole install? twice leaking condensate trap seems suspect. While it may not seem obvious the condensate drain and venting are related, both are open pathways to the fire side of the heat exchanger.

    Alan (California Radiant) Forbes
  • jeff123
    jeff123 Posts: 5

    It did happen immediatly after Silencer install

    I hope we can keep the silencer.

  • I once had a spider web clog a Lochinvar drain just where it went into the condensate pump. It backed up and came out the overflow port on the trap.

    Nice, clean installation. Pipes should be insulated.

    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    Gotta be a Massachusetts job