Can I drain one zone?

Options
JPL
JPL Member Posts: 18

I think this is an easy one. I have a cast iron boiler, primary-secondary piping, with four zones (each with its own circulator). There are isolation valves on each zone, and a boiler drain valve on the return side of each. One of the zones goes out to a three-season porch which we rarely use anymore. It has cast iron baseboards. The porch will get below freezing if the temps drop into the single digits or lower. I currently leave its thermostat set at 45 deg.

Can I just shutoff this zone, disconnect the circulator power from the controller, and drain it? I am not sure if leaving the cast iron radiators with no water in them is OK. That is, would I get rust/corrosion that would present a problem if/when it was used again in the future? Also, I can drain the return line but that will leave water from the circulator up to the rad on the supply side. Do I need to pull the circulator so I can drain the supply side completely (and then put it back in after draining)?

Any help is appreciated. I'd like to quit heating an unused porch if I can. But I don't want to do something that could cause a problem in the future.

Thanks all!!

Comments

  • hot_rod
    hot_rod Member Posts: 27,052

    as long as you can 100% isolate both sides. Use compressed air or a shop vac to be sure you get all the water out.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    GroundUp
  • JPL
    JPL Member Posts: 18

    Thanks, Bob!