L7224 Thermal Purge settings

Options
Robert_H
Robert_H Member Posts: 273

Servicing a Dunkirk DK4EXA075, fired at spec, 60-60B at 150psi. It is a direct vent system.

It is supplying the first floor of a three story house that the first floor was cut out as a rental and of course is oversized for the space. Cold start with no DHW

I service another boiler in the same basement so I have heard it cycle quite a bit. I don't think I have ever heard it run for more than three min, usually more like two min. The off cycles are usually 10 to 20 min. and the boiler doesn't cool off much in that time.

CA

MFR

Dunkirk

model

DK4EXA075

nozzle

60-60B

Pump Pres

150

Firing Rate

= 0.73

Tstack

345

O2

4.3

CO

48

EFF

86

ExAir

24

CO2

12.48

AT

46

Net Stack

299

This was at zero smoke, I forgot to save the data at Zero-1.5 % CO2 🙄. I'm sure at -1.5 the stack temp was higher but not by much.

High Limit is at 180, High Limit diff is maxed out at 20, which has no effect because the call for heat is usually satisficed before hitting high limit.

If I understand the manual for the L7224 , Anti Short Cycle (ASC) only effects the off cycle which is not the issue here. From what I have read here on HH Thermal Purge should be useful in this situation. If so, what would be good strarting settings for Thermal Purge Temperature Limit (tPL) and Thermal Purge Time Delay (tPt)?

Thanks!