Lock out on Carlin gas gun

Options
Dsisson
Dsisson Member Posts: 115

OK, another post about my boiler.

The Carlin gas gun has - within the last 2 weeks - gone into "lock out" mode 3 times. It's easily rectified by pushing the red button, but obviously there's a problem. Before I call a pro, is there anything I should check? Here's a photo, I can provide more if needed.

IMG_8249.jpg

Comments

  • HVACNUT
    HVACNUT Member Posts: 7,367

    Only advice would be for the pro to bring a 60200FR primary to upgrade the existing.

    Screenshot_20260115_130638_Samsung Internet.jpg

    It has diagnostics.

    szwedj
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,018

    Carlin gas burners are the best. If you having problems something else is wrong

    mattmia2
  • Steamhead
    Steamhead Member Posts: 18,365

    That's an older primary and they have been problematic. We routinely upgrade to the newer one that @HVACNUT mentioned and this solves the problem.

    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • HeatingHelp.com
    HeatingHelp.com Member, Moderator, Administrator Posts: 219

    I've deleted some comments on this discussion that were sarcastic, unhelpful, and stealing focus from the OP's question. Please follow our site rules and be respectful in your posts. Kindness looks better on everyone and I know you all have it in you. Thank you. - Erin

    Forum Moderator

    rick in Alaska
  • HVACNUT
    HVACNUT Member Posts: 7,367

    @Erin Holohan Haskell, I thought I asked the OP if he was ripping out his Carlin fired boiler, what does he plan to put in its place? How did that end up on the cutting room floor? That's a legitimate question. Maybe I'm thinking of a different thread. If so, apologies.

  • HeatingHelp.com
    HeatingHelp.com Member, Moderator, Administrator Posts: 219

    Sorry @HVACNUT I hadn't realized that was a question for the OP. My mistake.

    Forum Moderator

  • Jells
    Jells Member Posts: 643

    No, it was a question for me, as I commented I had the same burner. Not clear to me what infraction I made in the post other than stating my dislike of the device. And I made a specific helpful suggestion for OP to try. Deleted.

  • Dsisson
    Dsisson Member Posts: 115

    I didn't mean to cause a ruckus. I'm ordering the new control. The problem is so intermittent. I did find the carlin manual and checked the flame rod and igniter - both were misaligned so I aligned them according to the manual and reassembled. The problem came back though, so I think replacing the control is the next step and maybe it can tell me what the problem is at least.

  • GW
    GW Member Posts: 5,177

    it’s not a like for like swap out: you’ll have to read the instructions once or twice

    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Dsisson
    Dsisson Member Posts: 115

    I bought and installed the new control Carlin 60200FR. Unfortunately this seems worse than the old control.

    It initially worked but then gave a bunch of errors.

    Flame at post purge (twice) with uAmps 1.0 and 0.7


    eventually it got stuck giving a “no flame” error when I turned power off and on again. Pressing reset, then it gave a flame error with uAmps of 0.6. I disconnected the flame rod, still showed uA of 0.6.

    I cleaned and reinstalled the flame rod (taking care to adjust it per the manual). The errors persisted. I checked the connections but nothing changed.

    I reinstalled the old controller, it’s working. I guess I can push reset when I need to.

    Any idea what’s wrong?

  • mattmia2
    mattmia2 Member Posts: 16,297

    sounds like there's stray current somewhere

  • Dsisson
    Dsisson Member Posts: 115

    where should I look? Does this mean there’s a shorted wire? Bad ground? Another sensor that’s failed?

  • Big Ed_4
    Big Ed_4 Member Posts: 3,476
    edited February 16

    Flame rod needs to be cleaned.. Remove draw assembly and clean rod with fine steel wool . Return spacer under lock nut the way you find it. Set O2 around 5%

    There was an error rendering this rich post.

  • mattmia2
    mattmia2 Member Posts: 16,297

    why would that cause it to sense flame when there is no flame?

  • Dsisson
    Dsisson Member Posts: 115

    I did clean the flame rod. The control is sensing 0.6 uA with the rod attached or detached.

    It’s something else I think

  • Big Ed_4
    Big Ed_4 Member Posts: 3,476

    I am thinking O2 settings , what are the readings ?

    There was an error rendering this rich post.

  • pedmec
    pedmec Member Posts: 1,299

    You most likely have a crack in the flame rod insulator. voltage is leaking to ground

  • HVACNUT
    HVACNUT Member Posts: 7,367

    Are you sure it's lined up correctly through the diffuser plate, and assembly depth is correct? Its not hard to mess either of those up. Has a combustion test been done? Having that info might help.

  • Dsisson
    Dsisson Member Posts: 115

    with the boiler off, no flame at all, it’s sensing flame EVEN WHEN the flame rod is unplugged.

    I think it’s somehow seeing amperage from somewhere else.

    ??

  • Steamhead
    Steamhead Member Posts: 18,365

    That primary control puts a small AC voltage on the sensing electrode so when the flame is established it can rectify it into DC. I suspect the electrode has failed.