Why we use copper on relief valve discharges

Options

Comments

  • hot_rod
    hot_rod Member Posts: 27,056

    I think the current plumbing codes allow relief lines to be any material suitable to the discharge temperature? So I see the plastic tubes being passed now, looks like the same material as the dip tubes.

    Old codes required metallic discharge tube as I recall.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mad Dog_2
    Mad Dog_2 Member Posts: 8,462

    I dont use pvc for discharge, but better than this! Scary. Mad Dog

    GGross
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,034

    Hi, A benefit of copper is you don't get galvanic corrosion where copper meets the brass valve. A detail is the line is supposed to be run down to no more than six inches off the floor, so people are less likely to get burned. No doubt @EBEBRATT-Ed could comment on the wiring in the first photo too. 🤨

    Yours, Larry

    Mad Dog_2109A_5
  • pedmec
    pedmec Member Posts: 1,283

    mass plumbing code

    10.14.(6).(f).2.c

    c. The discharge outlet if the T&P relief valve shall be full-size and pipe using non-ferrous material or tubing rated to withstand the maximum relief valve temperature with no shut-off, toa fixture or a point to within twelve inches of the floor.

    Mad Dog_2Larry Weingarten
  • mattmia2
    mattmia2 Member Posts: 15,983

    in michigan it is worded such that water heaters need to be metallic but boilers just need to be rated for the working temp of the system.(at least as of the 2015 code we've been using for a decade, the new code may be different, not sure if we've actually are using it yet, it was adopted then some lawsuit paused it)

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,881

    @Larry Weingarten

    Octagon box with no cover and 4 runs of romex in it. Two runs of romex in one clamp only allowed if the connector is listed for it. Looks like one of those ground clips on the box edge to ground the box. I hate them but its code so I will let it go this time. But don't do it in my town ever again. And no romex staples seen. The romex has to be secured within 12 " of a box. I will have to look up the box fill for 4 #14s and 4 Grounds in a 4" octagon but I think its ok.

    @pedmec

    MA. is probably stricter than most states.

    Larry Weingarten
  • mattmia2
    mattmia2 Member Posts: 15,983

    how exactly does one find the listing for a romex clamp? they come loose out of a bin…

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,881

    @mattmia2 , everything has a listing. Even zip tys have to be listed for electrical

    non-metallic cable connector 842 Product Information

    Cable Connectors for NM • SE • SEU Cable

    Basic Information

    Part Number

    842

    Description

    NM cable connector zinc die-cast. 2 screw clamp type. Handles combinations of NM cable from #14 to #10. Up to 2 NM cables at one time. 3/4 Knockout. Also handles one 8/2, two 4/2 service cable.

    UPC-A

    018997008428

    Unit Packaging

    50pcs

    Standard Packaging

    500pcs

    Country of Origin

    made-in-usa.png

    Listing

    ulcsa.png