Slantfin Victory VSPH 120

Options
lakota
lakota Member Posts: 34

Boiler won't fire. 1107-12 control module. Goes through the sequences spark at ignitor but does not fire. What should the voltage read at gas valve. When sparking I have 12 volts from white to black and 12 volts from white to red. Is this correct

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,881

    Probably should be 24 volts. check the volts at the transformer. 120 v ac going in and 24v ac coming out.

  • lakota
    lakota Member Posts: 34

    Transformer volts 120 in 27 out. Bad control module?