Circulator Sizing

Options
ColdHouse
ColdHouse Member Posts: 94

I have a large zone in my four zone system. This large zone includes the entire concrete floor of my finished walkout basement of approx 1,650 square feet. It is made up of four loops, all 7/8" ID and all in the 285-295' length and attached to a common header and fed by one circulator and a check valve ahead of the pump and a common return header.

This configuration worked well for 15 years until a boiler failure and subsequent replacement of the boiler, which ended up upsizing the piping feeding the zone from 3/4' to 1.25". Once that project was complete all the zones were bled of any air and 3 of the 4 worked fine but the one for the basement. We bleed it multiple times and no circulation.

I am being told that the pump is undersized and we need to installl a larger pump? The current pump is 20+ years old, so I am not opposed to replacing it, I just want it to be sized properly if I do so. The current pump is a B&G 1/25 HP, Max head 15', Max flow 22GPM and 2940 RPM. What are the thoughts on a bigger pump or is there another issue that we are possibly missing? Did upsizing cause the issue?

Because we rarely use the basement since all our children have their own homes now, its not a emergency, but I would like to get the zone back up and running.

Comments

  • GGross
    GGross Member Posts: 1,767
    edited January 7

    the infloor loops (and really all of the zones) should be purged not just bled, offhand if I were asked about your scenario I would say airlock. all else the same upsizing the supply and return would not restrict flow, though there can be some downsides to a too large pipe size. Does the infloor zone work if your other 3 zone valves are closed? or still no flow?

    HydronicMikehot_rod
  • HydronicMike
    HydronicMike Member Posts: 289

    Why would you need a bigger pump if the last one worked? I agree with @GGross. Try purging that one zone until you get water thru it.

  • hot_rod
    hot_rod Member Posts: 27,053

    That 7/8" tube will take a lot of flow to purge. The fill valve, even in fast fill mode, if you have one, would probably not give you enough flow. Connect a garden hose to the system and use the high flow that it provides.

    Just keep an eye on pressure, stay below 27 pesi to avoid tripping any relief valves.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • ColdHouse
    ColdHouse Member Posts: 94

    Can you elaborate on purging vs. bleeding.


    I will have to try shutting down the other three zones and see.

  • hot_rod
    hot_rod Member Posts: 27,053

    Purging, or power purge with a pump, to me, is pushing enough flow thtough the tube to remove air and any dirt ot debris. To move heavy particles you need about 5 fps velocity. I would consider that closer to 1" pex size, so you need about 8 gpm flow

    \

    Screenshot 2026-01-07 at 3.06.31 PM.png

    Bleeding is more for removing a small air bubble trapped at a high point in a tank or radiator, for example

    Screenshot 2026-01-07 at 3.09.11 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    GGross
  • ColdHouse
    ColdHouse Member Posts: 94

    We were not using a external water source, so I will try purging and see if that takes care of te problem.

  • GGross
    GGross Member Posts: 1,767

    ideally you will need to isolate this zone to purge it properly. Typically purging a whole zoned system simultaneously won't work for the more restrictive piped zones like infloor heat. you need to isolate and purge each zone one by one, same way you do on a new install.

    hot_rod
  • ColdHouse
    ColdHouse Member Posts: 94

    So purge each of the loops within the zone separately? In this case there is four loops making up the zone, each have valves to isolate.

  • hot_rod
    hot_rod Member Posts: 27,053

    That is the for certain method, loop by loop. If you have multiple short loops 3/8 or 1/2" you can often flow more than one loop at a time.

    In either case the flow you have available makes a big difference. 1/2" fill valves set at 12 psi don't give a lot of flow. Fast fill position o the valve may get you 3- 5 gpm.

    A 1/2 bypass around a fill valve at 45- 60 psi will get you 10 gpm or more. That would allow for more loops to be purged together.

    The best indication is to put the purge hose in a 5 gallon bucket of water. Purge until all bubbles stop showing.