Thanks guys!!!

Options
hvactech75
hvactech75 Posts: 5
edited January 5 in Strictly Steam

Comments

  • mattmia2
    mattmia2 Posts: 18,399

    it is set up for hot water. looks like a gravity system unless there is a circulator somewhere we can't see.

    also looks sooted from lack of return water temp protection.

  • there is no circ pump anywhere, not sure how it would cir hot water?! Why does it look like its set up for hot water but also gravity steam? Sorry Im not crazy familure with steam boiler

  • mattmia2
    mattmia2 Posts: 18,399

    it isn't steam, it is gravity hot water. no circulator, the water moves by changing density as at is heated in the boiler and cooled in the emitters.

    if it is replaced it probably has to be converted to a pumped system and if it is a conventional boiler it needs low water return temp protection.

  • can a steam boiler be installed?

  • mattmia2
    mattmia2 Posts: 18,399

    no

  • KC_Jones
    KC_Jones Posts: 5,964

    Are you a contractor quoting a boiler replacement?

    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • mattmia2
    mattmia2 Posts: 18,399

    there is an aquastat on the outlet and an expansion tank. do you have a picture of a radiator? There is no sight glass or try cocks or pressuretrol on the boiler, right?

  • Grallert
    Grallert Posts: 1,237

    Miss Hall's School service mechanic, greenhouse teacher, dog walker and designated driver

  • trying to troubleshoot since it seems to have worked fine as a steam boiler for 2 years without any service

  • ChrisJ
    ChrisJ Posts: 17,763

    I'm going to assume you didn't install this?

    What do the radiators look like?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • mattmia2
    mattmia2 Posts: 18,399

    even as a steam boiler the new boiler is plumbed very wrong.

  • neilc
    neilc Posts: 3,213

    these 2 pictures are not the same boiler,

    are they ?

    known to beat dead horses
  • ChrisJ
    ChrisJ Posts: 17,763

    Interesting.

    Changed the name of the thread and deleted all of the photos etc.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    mattmia2pumpcontrolguyAlan (California Radiant) ForbesGGross
  • neilc
    neilc Posts: 3,213

    what the ?

    known to beat dead horses
  • Grallert
    Grallert Posts: 1,237

    No wonder I couldn't find it this morning. I has so many questions and not the bandwidth at the end of the day.