Thanks guys!!!
Comments
-
it is set up for hot water. looks like a gravity system unless there is a circulator somewhere we can't see.
also looks sooted from lack of return water temp protection.
0 -
there is no circ pump anywhere, not sure how it would cir hot water?! Why does it look like its set up for hot water but also gravity steam? Sorry Im not crazy familure with steam boiler
0 -
it isn't steam, it is gravity hot water. no circulator, the water moves by changing density as at is heated in the boiler and cooled in the emitters.
if it is replaced it probably has to be converted to a pumped system and if it is a conventional boiler it needs low water return temp protection.
0 -
can a steam boiler be installed?
0 -
no
0 -
Are you a contractor quoting a boiler replacement?
0 -
there is an aquastat on the outlet and an expansion tank. do you have a picture of a radiator? There is no sight glass or try cocks or pressuretrol on the boiler, right?
0 -
Not easily.
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0 -
trying to troubleshoot since it seems to have worked fine as a steam boiler for 2 years without any service
0 -
I'm going to assume you didn't install this?
What do the radiators look like?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
even as a steam boiler the new boiler is plumbed very wrong.
0 -
these 2 pictures are not the same boiler,
are they ?
known to beat dead horses0 -
-
what the ?
known to beat dead horses0 -
No wonder I couldn't find it this morning. I has so many questions and not the bandwidth at the end of the day.
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 168 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements