Triangle tube after recall- Supply Sensor
Had the recall done end of October for ignition and yesterday had a lockout due to Supply Sensor stuck closed. I hit reset and it started and ran all night. Is the sensor serviceable or needs replaced? Wiring issue? TIA
I’ve had the boiler since 2012, it’s been pretty reliable part wise but now that the company ceased operations, not sure how long parts will be available. Should I start buying replacement parts now or save up for a new boiler?
Comments
-
These are good questions I don't have an opinion on. So I'm bumping this as I sure there is someone who does.
Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver
0 -
The supply sensor is one part that I have had to replace on several TT units. With that fault code, it may not appear for a while but sooner or later it will appear again. The other part I have been needing to replace is the water pressure sensor. Even tho it still reads correctly, I have seen quite a few dripping with the water coming thru the sensor. So, I'd advise those two items for on hand parts. The unfortunate thing with TT has been that the parts seem unreasonably expensive.
0 -
Good to know. Thanks.
0 -
I should have added that both parts are quite easy to replace.
0 -
-
-
As someone posted on another thread. Try and buy the same boiler and strip it for parts. Obviously a bit tricky as you have to find one but they might be going for cheap money from a distributor who just wants to unload the stock.
0 -
the supply sensor is probably a basic thermistor. The manual gives you the resistance values so you can check it with an ohm meter
if the sensor did fail open , or a wiring glitch, a reset doesn't usually “fix” a bad sensor
Could be you have flow issues and the sensor was doing its job by tripping out on high temperature? Has the HX ever been deep cleaned ?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
The tech that did the recall cleaned both the burner and Hx.
0 -
Yes reset does fix it so it maybe a flow issue but I’m piped primary secondary and I have high mass radiant mostly so am operating 99% of time on the low temp curve.
0
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 122 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 116 Geothermal
- 169 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements