2015 TT Prestige boiler over-pressurizing and dumping water
Comments
-
I have a 2015 TT Prestige boiler. It is over-pressurizing and dumping water. It also has had a lot of air in the system. When I shut the dom wtr auto feed, it stays stable and I can bleed the air off with no reoccurrence…Is it just a bad DW auto feed valve?
0 -
@HeatingHelp please make this its own thread.
You are shutting off a feed only to a pressure reducing valve and not also to a heat exchanger for domestic hot water?
0 -
It's the makeup water supply to the closed system.
0 -
then the prv is leaking by. When fresh water is added and existing water is dumped out the relief valve, that fresh water that the prv lets in contains dissolved air, that is there your air is coming from.
0 -
0
-
Any thoughts?
0 -
it needs to be replaced or rebuilt.
0 -
That's what I figured, but wasn't sure if there was another internal source for the pressure / air.
Thank you ….
0 -
only the coil in an indirect water heater or the heat exchanger in a combi water heater but if it stopped if you closed the manual valve for the prv and there is nothing else on that valve then it is a pretty good sign that it is the prv.
0 -
that drip of water down the side of the prv isn't a great sign either.
0 -
@GPG77, welcome to Heating Help! I've created a new discussion for you here so that your question doesn't get lost within an older thread and to prevent confusion. Thanks.
Forum Moderator
0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 75 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements