Buffer Tank Port Selection
I'm redoing my mechanical room and managed to acquire a AO Smith TJV-120M at a very reasonable price. Hoping to use it as a buffer tank, but I'm a little conflicted about how to pipe it.
My first thought was to pipe it as a 3-pipe using a cross fitting from the top port (boiler in, heating out, and air vent). However, having the boiler input coming in through the top is probably going to disrupt the stratification in the tank.
The topmost side-wall port is located further down than I'd like (42" on a 62" tall tank) so it's not going to be getting the warmest water even if the tank is well stratified.
Alternatively, I could pipe it as a 4 pipe with the boiler coming in the side-wall port and the system piped from the top port, but then I'd lose the direct to load advantage of the 3 pipe.
Any thoughts on what might be preferable?
Comments
-
What type of boiler?
If you have a conventional non condensing boiler you could run the tank up to the highest temperature the system requires
Is it a single temperature system? Multiple zones? Zone valves or zone pumps?
For high temperature fin tube or radiators perhaps the tank goes to 160-180
Then you could pull loads off via an ODR control. This maximizes the tank drawdown.
Or the tank temperature could be controlled off the boiler ODR temperature, the tank just charges to whatever the ODR controller determines
The is a great tank to score! It has nice connection options.
with that large top connection you could drop a sparge tube in, a capped nipple with slots cut around.
A double tapped bushing supply house.com or RW Beckett has them.
I think the 4 pipe is best for wood boiler systems, it acts as an over temperature dump as much as a buffer.
2 or 3 pipe direct to load has a few advantages as you mentioned. Here is a simplified sketch.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks @hot_rod for your suggestions.
Boiler is an IBC mod-con. Majority of the house is fin-tube baseboard with zone valves, then a bit of radiant in the basement. My plan is to have the tank controlled by ODR from the boiler with the reset curve tuned at the higher temp for the baseboards. The radiant zone will be mixed down from the tank temp.
Sparging tube is an interesting idea I hadn't considered before. I'm in Canada (BC) and locating a double tapped bushing is proving a little tricky. Might be able to improvise something by skimming off the end stop on a reducing bushing with the lathe effectively turning it into a slip fitting. Stackup would be 1-1/4" copper from boiler → 1-1/4" x 1-1/2" bushing (converted to slip) → 1-1/2" sweat x MIP adapter → 2" x 1-1/2" reducing bushing → 2" tee → buffer tank with the 1-1/4" continuing through the center of the whole stack and into the tank as the sparging tube.
Another question I had is where to put the thermowell. Usually I see them around mid-height so the 2" sidewall port might be my only option?
0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 427 Carbon Monoxide Awareness
- 119 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 165 Indoor-Air Quality
- 3.7K Oil Heating
- 75 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.6K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements