Attic blower times.

Options
tmtruett
tmtruett Member Posts: 27

Hello I have a oil boiler and forced air. 2 handlers one in basement and one in attic,

My question is the blower cycling time of attic unit. When heat is first called it runs for over 3 minutes. When temp reached I have timed it to be a pattern of approx 2 and half minutes off and only 40-45 seconds on. Not sure if I am over thinking this but thought I'd ask any veterans out there if that is "normal". Took pic of the stat setting and model if at all helpful. Thanks

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,279

    I would suggest that your heat anticipator setting or cycles per hour setting in the thermostat is incorrect

  • HVACNUT
    HVACNUT Member Posts: 7,172

    Can you explain the 3 minutes run, two and a half minutes off, 40-45 seconds on thing in more detail?

    With that setup, the strap on aquastat is set to bring the fan on once water temperature reaches 140°. I'm not familiar with that control. Check the cover to see if there's an adjustable or fixed differential.

    As an example, the fan comes on at 140°. Say the aquastat differential is 20°. It should be mounted on the return side of the coil. If the fan throws off so much heat it drops the return temperature to 120°, the fan will turn off until return temperature reaches 140° again. When the thermostat satisfies, the fan will continue to run until until the return temperature reaches 120°. That's where the anticipator @EBEBRATT-Ed mentioned comes into play.

  • tmtruett
    tmtruett Member Posts: 27

    Hello. sorry I was not getting email notification

    So when heat is first called for, say turn it up from 60 to 65, it will run for an 3-4 minutes, off for 2 or so minutes and repeat until temp reached. Once reached it will run for only 45 seconds and then stay off for 2 1/2 -3 minutes and repeat. That run time seems short to me. In the pic, I removed the cover of the aquastat to check wiring connections. Not sure it is set correctly, it is adjustable

  • mattmia2
    mattmia2 Member Posts: 15,191

    What kind of thermostat? You have to figure out which control is shutting it down. That cycle rate sounds a lot like a mechanical thermostat with the cycle length set way too short.

  • mattmia2
    mattmia2 Member Posts: 15,191

    If it were a limit control or aquastat the cycle length probably wouldn't vay much with a 5 degree difference in room temp but the anticipator on a thermostat would.