Where to connect Outdoor sensor on WM CGa4 PIDN Series 3 boiler

Options
mariusz6100
mariusz6100 Member Posts: 9
edited November 27 in Radiant Heating

Hello, I am having difficulty finding information on how to connect the Outdoor Temperature Sensor Kit, 381-356-586 to CGa4-PIDN series 3 boiler control unit. There is no drect plug in where I can connect the harness provided with the kit and there are no instructions how to connect it. I have not found any information whether an outdoor reset kit is also reuqired. From what I could find, it would seem I should be able to connect the sensor to the contiol unit directly.

The control unit has ODT terminal for 1 wire which seems to be outdoor temperature sensor at C9-1 (same as P9-1 on the other wiring diagram), but I have no idea where I should plug in the second wire and whether C9-2 24VAC Common is the right spot (same as P9-2 on the other wiring diagram). Or I may be misreading the diagram all together.

Any heklp is apreciated and I am including pics of the diagram and control board.

Here is the manual diagram, there is no connection to the harness on the control board:

image.png image.png


Here is the diagram from the boiler

IMG_1901.jpg IMG_1902.jpg



And here is the pic of the control unit

IMG_1906.jpg IMG_1915.jpg IMG_1914.jpg IMG_1916.jpg

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 19,602

    I am guessing.

    I think you connect to the orange plug at the top left corner of the control. But it looks like you already have a wire connected to the ODT terminal a red wire. I would guess the other ODT wire would connect to the common.

    I will check further. Where does that red wire go now?

  • hot_rod
    hot_rod Member Posts: 26,604

    It sure looks like the two right side terminals 1 &2, on the orange block?

    Screenshot 2025-11-27 at 8.46.02 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mariusz6100
    mariusz6100 Member Posts: 9
    edited November 27

    Yes I think the orange block 1 and 2 (C9-1 and C9-2) right now, the sensor is connected to 1 (red wire) and 4 (white wire) so moving the white wire from 4 to 2.

  • HVACNUT
    HVACNUT Member Posts: 7,235
    edited November 27

    You actually have a Series 4. I see a different control module used in the Series 3.

    Screenshot_20251127_095451_Drive.jpg Screenshot_20251127_130458_ProTools.jpg
    mariusz6100
  • mariusz6100
    mariusz6100 Member Posts: 9
    edited November 27

    You are correct, apologies, it is the Series 4 boiler with the new Unity-CI control without the plug in terminal for the outdoor sensor

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 11,575

    C9-1 and C9-2 is the place to connect that ODS

    Screenshot 2025-11-27 at 2.17.06 PM.png

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    mariusz6100