Old Richmond Furnace looking to replace Fan limit switch.
MrMagic
Member Posts: 17
I have a old Richmon Furnace looking to replace combo limit Fan limit switch. Blower Fan comes with call for heat but will not shut off.
14029c 1115 1 G14
14028F 1002 1 G14
0
Comments
-
-
Measure the insertion piece. Resideo Fan/Limit. It comes with instructions when there's two different voltages, which you have. You'll have to cut a jumper.
0 -
Thanks. Ok I'll measure the prob length this weekend.
0 -
Probably will have to drill some new holes to mount it, don't go too deep and use short screws, you just want to drill through the cabinet, not in to the heat exchanger.
0 -
Honeywell L4064B. They make several models. Insertion can be 5 1/2", 8" or 11" Fan/limit control