Hey everyone, I don't know much about controls and was looking to get some input. This is for my radiant floor heat system at the car wash. It is two separate slabs that I will be heating, each has their own manifold and system pump.

I have two navien NHB-150H boilers that will heat the system.

A tekmar 073 sensor in each slab will read the temps. I'm really just trying to keep the bays from icing over and to be warm enough to melt snow when it blows off peoples cars.

I'm thinking to have the Navien boilers control their own boiler pump.

My idea is to have a tekmar 170 set point controller for each of the 2 slabs and sensors. Then wire those into a tekmar 302P relay switch to control when the manifold pumps turn on.

Another option is to get a tekmar 301P for each of the set point controllers.

What advice or input do you have? Should I have the tekmar 302P control the whole system, including the boiler pumps as well? Get something else instead? Again this isn't a super complicated system. But sometimes one slab might be a little colder or warmer than the other based on people using them.

Also any input on the 2 navien boilers. I have the cable to connect them.

I also don't want the system to turn on when it's above 36 degrees outside or so

Comments

  • mattmia2
    mattmia2 Posts: 18,399

    I think tekmar has more general purpose controllers that be programmed to do it all in one control.

    MichaelT
  • hot_rod
    hot_rod Posts: 28,705

    You need those slab sensor to be the main control if you plan on idling above slab freezing temperature? So you need the two sensors, two 170 control.

    Actually all you need is the 150 setpoint controls, save some bucks. Unless you want the WiFi fuction?

    Screenshot 2025-10-16 at 3.52.20 PM.png

    Screenshot 2025-10-16 at 3.53.01 PM.png

    You could just let the pumps run. That way any solar gain on the slab gets circulated.

    Or the pumps wire to the boiler system pump output, so the pump starts when the boiler calls.

    The setpoint controls just call on the boiler. The 170 or 150 needs power from a 24V source, then S1 and com for the sensor. XX goes to the boiler

    Did the boilers come with outdoor sensors? If so maybe that function to shut off the boiler above 38° If it has that range of adjustability. If not you need a sensor in the bay to know when it is above 38. Although the air could be 38 and the slab still cold enough to ice over?

    I'd just try setting the differential on the 150 on at say 34-35°, Off at 38 or so.

    Did you install the 073 sensors in a conduit so it can be replaced? Sensors fail from time to time.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    MichaelT
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,948
    edited October 2025

    Hey everyone, I don't know much about controls and was looking to get some input. This is for my radiant floor heat system at the car wash. It is two separate slabs that I will be heating, each has their own manifold and system pump.

    You stated: I have two navien NHB-150H boilers that will heat the system.

    The Navian boilers have control systems that can connect directly to slab sensors as the means to turn them on and off. they have outdoor reset capability and they have a Warm Weather Shut Down (WWSD) feature

    You asked: "A tekmar 073 sensor in each slab will read the temps. I'm really just trying to keep the bays from icing over and to be warm enough to melt snow when it blows off peoples cars.

    I'm thinking to have the Navien boilers control their own boiler pump.

    My idea is to have a tekmar 170 set point controller for each of the 2 slabs and sensors. Then wire those into a tekmar 302P relay switch to control when the manifold pumps turn on.

    Another option is to get a tekmar 301P for each of the set point controllers"

    I might suggest that you look at the Tekmar 654

    What advice or input do you have? Should I have the tekmar 302P control the whole system, including the boiler pumps as well? Get something else instead? Again this isn't a super complicated system. But sometimes one slab might be a little colder or warmer than the other based on people using them.

    You Asked: Also any input on the 2 navien boilers. I have the cable to connect them.

    Having two boilers that can do the job for both slabs is better than isolating one boiler for one slab and another boiler for the other slab. Properly valved, you can have one boiler do both slabs at the same time and the control for each slab will regulate the boiler water as needed. If one boiler goes down and the other boiler is isolated, you are stuck with no Ice Melt on the one system. You can heat both slabs while the inoperable boiler is getting repaired or waiting for parts. Also as the system gets up to temperatue, only one boiler may be enough to maintain slab temperatures

    You asked: I also don't want the system to turn on when it's above 36 degrees outside or so

    That's easy, set the WWSD at 34°. If the Navian WWSD does not go that low, then add an outdoor temperature control that will power off the entire system when the temperature is above 36° and comes back on at 34°

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • After a review of the Navian boiler WWSD, the lowest setting is 50° which is too high for your purpose

    After a review of the Tekmar 654 snow melt control the WWSD feature is able to be set so that when the slab temperature is able to melt snow without heat input, the boilers will not operate. This is better than your suggestion of a random temperature of 36°F. If the slab has retained heat from a warm sunny day and the outdoor temperature drops to 30°F the boiler may not be required. Also of the slab temperature is cold and the outside temperature is above freezing, the rain may actually land on the slab and freeze on contact. This control will eliminate that as a problem.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Posts: 28,705

    to use the tekmar snow control you would want the snow sensors in the slab

    It is an expensive sensor

    IMG_1209.jpeg

    It is an expensive control, sensor, cup, and control. And you need two?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • 109A_5
    109A_5 Posts: 4,759

    That's expensive wire, $3.95 / ft. more for the longer version. I wonder how that sensor would hold up in that car wash environment.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    MichaelT
  • I was thinking to get the 170 for the wifi function. Might be overkill but would be nice for some alerts.

    Yes the boilers did come with outdoor sensors. I was thinking the 170 can be programed to turn things off when above 38 degrees. I know some of tekmar controls can even use local weather temperature. But I think I can install an outdoor temp sensor to it. Yes I did install the 073 sensors in a conduit in case I need to replace someday.

  • That was exactly my thoughts of putting in two boilers instead of one larger boiler. So that if one goes down for repair I can still heat both slabs. I do have it set up like that. Yes then only one of the boilers could maintain the system.

    Okay, I did not think about that scenario Ed, good advice. Do you know if the tekmar 170 is capable of that as well?

    That snow sensor is expensive, probably wouldn’t last very well in a car wash though. 

  • "That snow sensor is expensive, probably wouldn’t last very well in a car wash though. "

    I don't believe the actual sensor would be a problem in a car wash. it is made to be outside in the weather so placing it inside a car wash at one end or the other where the soap and other cleaning agents are not present would be the preferred design.

    Do you know if the tekmar 170 is capable of that as well?

    I do not believe the Tekmar 170 does all that the Tekmar 654 can do.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Here is the info from:

    The Wi-Fi Setpoint Control 170 provides precise temperature control of a one-stage heating or cooling system. When connected to the Internet, the Watts® Home mobile app allows the setpoint control to be controlled remotely. An Away mode is quickly and easily accessed to provide energy savings when the heating or cooling system is unoccupied. The setpoint control can be used to control the heat for an indirect domestic hot water tank, a pool, a hot tub, or small outdoor patio, as well as provide cooling for a wine cellar.

    The Snow Melting Control 654 is designed to operate electric or hydronic equipment to melt snow or ice from any surface including driveways, walkways, patios, business entrances, parking ramps, loading docks, hospital entrances, helipads or car wash bays. The surface temperature for snow melting is controlled automatically to reduce operating energy costs. The 654 has an automatic start and stop function when used with the Snow/Ice Sensor 090 or 094. Automatic start with a timed stop is available when used with the Snow Sensor 095. The 654 can operate a dedicated hydronic boiler or a mixing device. Isolation relays are required to operate line voltage pumps. Electric systems require a separate GFCI and electrical relay contactor  

    Looking at the two different controls I see that the 170 is basically a WiFi thermostat that you can check the status of an on/off system over the internet, based only on temperature. This will require constant monitoring to do the job you need it to do.  If the outdoor temperature is such that the slab that you do not want ice to accumulate on is at the set point you select, then the 170 will operate the boiler even if there is no need for boiler operation.  It will only operate based on the temperature you select and the sampling of the temperature by whatever sensor you attach to it.

    The 654 will measure not only temperature of the slab, but will also make a decision on boiler operation based on the presence of ice or snow when using a 5 wire sensor placed in the wash bay slab. If there is no ice at the selected temperature, then the boiler will not operate.  So, the 090 sensor that does all the savings by keeping the boiler off if there is no ice, does not connect to the 170.    It does connect to the 654.    There is a less expensive 095 aerial control that may or may not work for your application.  The aerial snow sensor will not operate the boiler if there is no precipitation (SNOW). The car wash always has water on the floor during operation even if there is no precipitation otherwise.  

    So, I believe the floor sensor will be more accurate. However, if you strategically locate the 095 where the clean rinse water or clean prewash water will make itself known to the 095 then you could go that route.  The aerial sensor is not confined to the concrete slab and is less expensive and you can have an extra on hand if needed.  

    You get what you pay for.  If you don't mind constantly checking the system and adjusting the temperature accordingly then go the less expensive route.   If you want to take a vacation (or hospital,wedding, or funeral) from the car wash business in January, then you need the control that you can set and forget. 

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    MichaelT
  • hot_rod
    hot_rod Posts: 28,705

    unless you put the sensor cup 091, in the slab along with a conduit, the snow and ice sensor may not be an option.

    The task is pretty simple in a car wash bay, keep the slab above 32F. No need to make it. More complicated.

    IMG_1245.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    MichaelT