Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!

Carlin Hot water heater keeps going on and off.

Options
Shuga
Shuga Member Posts: 25

Carlin Hot water heater, Model EZ-1 Has been acting up recently since last oil delivery. I did not go dry, Regular scheduled delivery. The Water heater unit keeps putting me into lock out mode. I bleed the system and reset it, it'll start back up with a green blinking light. The light hasn't gone solid green. But it works for a few hours and then shuts down and puts itself back into lock out mode. When it works, there are no lights. I can't figure this out. It's getting extremely

annoying to have to keep restarting it every few house. Any ideas?

Comments

  • Shuga
    Shuga Member Posts: 25

    Photo of the unit above ^

  • mattmia2
    mattmia2 Member Posts: 17,571

    you need a good oil burner tech. when was the last time it was cleaned and adjusted?

    techforlife
  • Shuga
    Shuga Member Posts: 25

    I'm my own tech lol. It was fully replaced with a brand new unit in 2021

    HVACNUT
  • mattmia2
    mattmia2 Member Posts: 17,571

    what are the combustion and draft numbers?

  • Shuga
    Shuga Member Posts: 25

    Where would I find that?

    HVACNUT
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,543
    edited October 2025

    Those numbers are found using the combustion analyzer that your Tech should have used on the most recent service. If your Tech does not have one of these Combustion Analyzer things along with a Smoke tester for oil heating work, then I would fire him and hire someone that knows how oil burners actually work.

    There are several reasons for a primary control to go off by the safety lockout. …and did you know that you are only supposed to RESET ONLY ONCE. That is taught in every technical school when the students are learning about oil heat primary controls. I'm just saying that it sounds like your Tech does not subscribe to that well known rule of the trade. If the control locks out after you have reset it once, then the knowledgeable tech would take the burner apart and find the cause.

    1. Partially plugged oil filter
    2. Partially plugged fuel pump screen
    3. Partially plugged nozzle
    4. Dirty ignitors
    5. Ignitors out of adjustment
    6. Ignitor insulators cracked
    7. Ignition transformer or electronic ignition failing intermittently
    8. Incorrect combustion air adjustment
    9. Incorrect fuel pressure
    10. Partially plugged fuel line from the tank.

    These are just the first 10 reasons that a technician with over 40 years experience might think of off the top of his head. There are many more reasons.  Maybe these reasons will help to refresh your technician’s memory about what might be the reason for the flame failure lockout!

    But don't be too harsh on your technician, everyone needs to start somewhere!

    Mr. Ed

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    mattmia2szwedj
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,543

    I'm not making up this "RESET ONLY ONCE" thing…. many different manufacturers of primary controls place these instructions in the literature that comes with the control and some even print it on the control itself

    Screenshot 2025-10-09 at 3.35.00 PM.png

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • HVACNUT
    HVACNUT Member Posts: 7,539

    You find it on your combustion analyzer. Its DIY, until its not. Find an oil burner tech.

    techforlife
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 20,554

    Oil appliances are not like refrigerators, toasters or vacuum cleaners. You don't just plug them in and expect them to work.

    They need to be cleaned every few years and tuned and adjusted like a car they need professional attention.

    mattmia2
  • techforlife
    techforlife Member Posts: 128

    You are your "own tech" until you can't fix it. Then you need a real tech. who has an experienced diagnostic approach to the issue.