Welcome! Here are the website rules, as well as some tips for using this forum.

Need to contact us? Visit https://heatinghelp.com/contact-us/.

Click here to Find a Contractor in your area.

If our community has helped you, please consider making a contribution to support this website. Thanks!

Will I have to drain my whole heating system?

Options
scatgo
scatgo Posts: 102
edited September 2025 in THE MAIN WALL
leak.jpeg

Will I have to drain my system to replace the section of leaking pipe between the supply valve and what i think is a pressure reducing valve? And what is the red gizmoe after the PRV?

Comments

  • hot_rod
    hot_rod Posts: 28,706

    is there a valve to the right if the two red valves? You need to isolate both sides.

    The red valve on the right is a pressure relief valve. If you have one on the boiler you do not need that

    You should however have a backflow preventer at the fill valve

    And if you do need to drain down, replace the relief valve on the boiler

    Buy a combination fill/ BFD

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Posts: 18,399

    if it is the relief valve there should not be a valve between it and the boiler.

    scatgoEdTheHeaterMan
  • Will I have to drain my whole heating system?

    YES!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    scatgo
  • scatgo
    scatgo Posts: 102

    Thanks for the help everyone.

    Peace