Thermolec th22 with tekmar 519 thermostat

Hello guys ! I have bought a thermolec boiler for my garage floor that comes with a tekmar 519 thermostat. Everything hooked up to the electricity but i have hard time to have the system working with the thermostat. Everything work followong the troubleshooting guid thermolec give me pump heater etc.

His anybody here have already wired up this kind of boiler here some picture thermostat showing temp but when he ask for heat nothing happen. My seller can't help really much.

https://www.watts.com/products/hvac-hot-water-solutions/controls/thermostats/519

https://www.thermolec.com/en/products/electric-boilers/mini-boiler

Thanks in advance

1000012169.jpg 1000012167.jpg 1000012168.jpg 1000012087.jpg

Comments

  • hot_rod
    hot_rod Member Posts: 25,531

    I think the thermostat C&R wires to C and W-1 on the boiler board.

    Screenshot 2025-08-29 at 1.09.43 PM.png

    Is outdoor reset connected? It may be too warm to allow it to fire.

    Screenshot 2025-08-29 at 1.10.49 PM.png Screenshot 2025-08-29 at 1.13.32 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • 109A_5
    109A_5 Member Posts: 2,596
    edited August 30

    Looks like your wiring is incomplete. Nothing is connected to the 'C' terminal (at the Red arrow).

    From the manual.

    image.png image.png

    I suspect if the Orange arrow is the thermostat cable (Red, Black and White wires), you need a wire connecting the low side of the 24 VAC (Thermostat cable Black wire) at the Right hand circuit of the 24 VAC terminals at the Yellow arrow to the C terminal of the TH22 unit at the Red Arrow (other picture above).

    image.png

    In the picture below the Blue line is representing the wire I believe is missing.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 2,596
    edited August 30

    Additionally, It looks like the 24 VAC thermostat control wiring installed by the installer can be inserted and secured into the terminal strip on the bottom side (Red arrows). Not all jammed into the top of the terminal strip. Yellow arrows are an example of using both the top and the bottom connections of the terminal strip. The screws are connected vertically inside the terminal strip, in this example.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • 109A_5
    109A_5 Member Posts: 2,596

    It seems the TH22 may have the 24 VAC power connected to it and to trigger the boiler they may switch the Low side (C to W1) of the 24 VAC instead of the typical Hot side R or Rh to W contact closure.

    The manual is kind of vague and apparently does not show the use of that type of thermostat you have, the thermostat type that requires power.

    The jumper from R th Rh in the thermostat would be removed first.

    I suppose the other way this could go is; using your wire colors is Rh on the thermostat goes to C on the TH22, Red wire. W on the thermostat goes to W1on the TH22 using the White wire. That leaves the Black wire to provide power to the thermostat from the terminal strip at the bottom of the cabinet.

    If the C on the TH22 is actually the common or Low side 24 VAC terminal the black wire would go to the Hot or High side of the 24 VAC at the bottom of the unit's cabinet.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System