Condensate Piping- One Pipe

Suchitapage
Suchitapage Member Posts: 16

Hello,

I am working on this building which has one-pipe steam system. I came across this condensate piping arrangement. The condensate return is a dry return until the very end and it drops abruptly near the boiler (have attached the photos). So would like to know if this a very common piping arrangement?

Also, how does this system performs because I couldn't see a hartford loop ?

Thank you.

20250828_142805186_iOS_-_Copy.jpg 20250828_142815118_iOS.jpg 20250828_142819790_iOS.jpg 20250828_142826926_iOS_-_Copy.jpg 20250828_142829301_iOS.jpg 20250828_142843353_iOS.jpg 20250828_142904844_iOS.jpg

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,415

    Need to take pictures from farther back so we can see the whole…..picture!

    It looks like you have a bunch of return lines that drop down below the boiler water line before they connect.

    mattmia2Intplm.
  • Suchitapage
    Suchitapage Member Posts: 16

    I have added some more photos further back from the boiler.

    20250828_132838354_iOS.jpg 20250828_132742669_iOS.jpg 20250828_132744173_iOS.jpg 20250828_132748237_iOS.jpg 20250828_132749310_iOS.jpg
  • Suchitapage
    Suchitapage Member Posts: 16

    Yes, but they also have a steam pipe getting connected to the return header. In the below photo, the pipe furthest from the viewer is a steam pipe and the two pipe closest looks like a condensate pipe. This is getting connected to the boiler

    image.png
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,415

    Cant see it but the steam to the return header is probably a drip from the steam supply. Nice ST Johnson Burner. The pipes in the air are difficult to see

  • 109A_5
    109A_5 Member Posts: 2,610

    I suspect in this case the wet return is so short (and completely visible) there would be no benefit in adding a Hartford loop.

    " they also have a steam pipe getting connected to the return header " This may be the Equalizer pipe.

    The system may benefit from better main venting.

    image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Intplm.
  • Suchitapage
    Suchitapage Member Posts: 16

    Is there any benefit of piping this way than the conventional way of dropping pipe and having long wet returns and Hartford loop?

  • mattmia2
    mattmia2 Member Posts: 13,935

    Depends more on where you have space for returns. The high returns won't rust out unless your boiler is throwing water in the mains. You can locate the vents centrally at the boiler.

    Suchitapage
  • 109A_5
    109A_5 Member Posts: 2,610

    Much less wet return pipe to fail and maintain. It may have just fit into the buildings structure better, without having to bury the wet return and make it hard to maintain and find leaks.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System