I have a W/M plus 80 indirect hot water tank connected to my Weil McLain boiler oil furnace.
Could someone please help me understand 2 things:
- There’s an auto air vent on top of the hot water tank which is leaking and I want to replace it. Is that connected to the boiler line (12 psi) or is it connected to the domestic water (60 psi)?
- The manual
Comments
-
What you have there is a Triangle Tube Smart Series tank within a tank indirect water heater branded by Weil Mc Lain. The domestic water is in the inner tank and the boiler water surrounds it in the outer tank. Best design in my mind and my 60-gallon model is twenty-four years old. You could replace the air vent with the Triangle part number P3KITAV02 or a Taco 4004.
0 -
If I remember right, its a full 3/4" Hy-Vent.
If there are isolation valves on both the supply and return for the water heater, you can close them, then open the purge valve (with hose and bucket) for that loop to drop the pressure to 0 psi.
You don't need to order from Triangle Tube, you can use SupplyHouse and look for a Taco 3/4 Hy-Vent.
Just making sure. You have a bladder type expansion tank, correct? Not a compression tank in the ceiling.
1 -
I thought those vents were 1/2”
Regardless you could increase or decrease the pipe size if you get the wrong one
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If you don't want to wait for the vent to be changed, you can tighten the cap finger-tight. It's similar to a bicycle valve.
0 -
The vent is on the Boiler water not the domestic correct?
0 -
Yes, on the boiler side.
0 -
It’s 1/2” female npt. Last time I bought one Triagle Tube had changed and provided a manual vent. I believe that leaking auto vents had damaged too many heaters since the outside tank can rust. I like the auto vents but they require maintenance. You can go either way.
0 -
this is the vent. It appears to be a 1/4 mounted on a 1/2 adapter.So this is on the boiler side, I just need to shut off the isolation valves on the boiler side, drain the water a few drops to relieve the pressure and then unscrew and replace right?
0 -
this model comes with a safety cap to stop a drip if the vent fails
Ideally if you have a good air purger in the system that auto vent works for the first filling. Or if you drain and refill
If air comes out on a regular basis, somehow air is getting in to the system?
If air is entering somehow, that will cause a lot of rust and corrosion, that is a plain steel tank
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Yes. And, I see, most likely, a half-inch by eighth-inch bushing under the vent. I would be ready to change it with both sizes, just in case something breaks.
0
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 426 Carbon Monoxide Awareness
- 116 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 109 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 994 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements