Accidentaly hit PEX with nail. Above subfloor radiant heat

WillC
WillC Member Posts: 28

Hi there,

I have an above subfloor heated floor that I am doing myself.

Flooring nail didn't go straight and punctured PAP PEX. I can't replace the loop, unfortunately PEX needs to be fixed. What's the best way to approach this?

I was thinking to cut the plywood around the puncture, cut the PEX and use a brass coupling with 2 clamp rings. (is a crimp ring better? Should I install a heat shrink sleeve?)

I am worried about expansion and the connection getting loose over time. If it matters, I have also access to this part of the subfloor from the basement ceiling (underneath).

I have included a picture of the "before the flooring install".

Thanks

Screenshot 2025-08-05 at 6.42.59 AM.png

Comments

  • hot_rod
    hot_rod Member Posts: 25,407

    Just a coupling that fits that type of tube is fine. No harm in heat shrinking it also. That is mostly for repairs in concrete pours.

    Maybe make a map of the exact location, for peace of mind.

    What brand of tube is it? Do they offer a crimp coupling, or just compression style?

    On my Warmboard installs I would get a roll of butcher paper, lay it across the room to make a map of the exact tube location. pics or drone shots work well also.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    jamplumb
  • WillC
    WillC Member Posts: 28

    thanks for the reply. I called them and they do have a specific repair kit, I’m gonna get it tomorrow.

  • Phil_17
    Phil_17 Member Posts: 179

    I had a similar problem about 15 years ago when our plasterer managed to slit the PAP tube in a warmboard installation. I wound up shortening the loop by routing a new return into the floor which provided slack to effect the repair. I cut out the damaged portion and poked both of the ends through the subfloor into the cavity below where I used the manufacturers recommended compression fitting to splice the tube in a location where I could more easily get at it if I ever had an issue in the future (thinking it would be a lot easier to cut and patch some drywall from below than to pull up and repair a hardwood floor). I haven't had any issues so far…

    PeteAAlbany Chris