Welcome! Here are the website rules, as well as some tips for using this forum.

Need to contact us? Visit https://heatinghelp.com/contact-us/.

Click here to Find a Contractor in your area.

If our community has helped you, please consider making a contribution to support this website. Thanks!

Weird Noise from 3/4" Wilkins 350XL Double Check Valve

Options
FredoSP
FredoSP Posts: 124
edited July 2025 in Plumbing

Hi All,

A couple of days ago I had my annual backflow device tested and it passed, no issues. Today I started to hear this strange humming noise coming from the basement when I turned on the kitchen faucet. I then tested the upstairs sink faucets, same noise. I tracked down the noise to be the backflow device. To me it sounds like air is trapped? The noise goes away when the faucet is shut off. Can anyone give me any suggestions on what to do? The backflow device could be ten years old, maybe its end of life?

3/4" Wilkins 350XL Double Check Valve Assembly (Lead Free)

I have uploaded a 7 second video of the noise.

LINK TO VIDEO

IMG_3511.jpg
Long Island, NY

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,951
    edited July 2025

    I find that most humming happens when they forget the words. If you can find the proper sheet music with the right lyrics, the humming will stop.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,329

    @FredoSP

    Maybe open every faucet in the house wide open and run it a little.

  • hot_rod
    hot_rod Posts: 28,708

    did they rebuild it or just a test and recertification?

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • FredoSP
    FredoSP Posts: 124

    Thanks Ed but that didn't change anything.

    They just did the annual test that's required by my local water authority. I was in the basement watching. One guy was holding a flavor flav inspired gauge and a line or two was connected to the backflow device. The other guy was entering the numbers in the iPad. It was not making this noise before or during the test. I only noticed this later on in the day after they left.

    Long Island, NY
  • Intplm.
    Intplm. Posts: 3,162

    On your device, you have three test cocks. They are the small valves with the little black plugs. Remove the plugs and, one at a time, run water through the test cocks. Let it run…spray, for about five seconds or more. See if that helps remove the noise.

    If that doesn't help, check to see if a hanger/support supporting the device is loose or missing.

  • FredoSP
    FredoSP Posts: 124
    edited July 2025

    Thanks for the suggestion but it didn't do anything to help with the noise.

    I'm wondering if something internally has failed or is worn out. I looked through my receipts and found this device was installed in 2014, so maybe something like an o-ring or one of the springs inside the check valves are acting up, or even sand or a small pebble made its way in?

    It looks like I can purchase a new housing assembly that has the two checks and o-rings. It's a fraction of the cost of replacing the whole thing. What do you think?

    wilkins_1.jpg
    Long Island, NY
  • Intplm.
    Intplm. Posts: 3,162

    If you have found the direct replacement part and the noise is that much of a nuisance, why not replace it? If nothing else has worked and you a confident that the valve is the source of the noise? Why not.

  • hot_rod
    hot_rod Posts: 28,708

    there really is not much inside, two self contained spring checks.

    Very easy to disassemble and clean, but you do loose the certification if you tear it down.

    I would have the two replacement checks on hand if you open it up

    IMG_0672.jpeg
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • FredoSP
    FredoSP Posts: 124

    Thanks guys. I ordered the replacement today and will report back once its installed.

    Long Island, NY
  • FredoSP
    FredoSP Posts: 124
    edited July 2025

    A follow up … I installed the replacement cartridge and its quiet as can be! I will take the old one apart later, but I would guess that one of the seats failed. I guess that's why the sell these kits because nothing lasts forever, except for your marriage 😎

    Long Island, NY
    Larry WeingartenIntplm.
  • mattmia2
    mattmia2 Posts: 18,399

    I suspect a seal disc of some sort is degraded and curling up and vibrating like a reed.