Snowmelt magician!

Options
Simply Rad
Simply Rad Member Posts: 209

I heard the phrase I am a technician and not a magician. Well now I understand. This picture show the homes entry stairs detail. I have to tube the stairs and some how melt them. The insulation is 2” down, shown by the red line. Also, I am not able to run tube in the bull nose detail due to lack if concrete and lighting detail. Not sure how I am going to melt and control this. SMS will be in the easy to melt landing spot. Concrete will be exposed on all sides bottom. Lots to overcome here.

Jeffrey

IMG_2556.jpeg
Jeffrey Campbell

Comments

  • Allislandradiant
    Allislandradiant Member Posts: 41

    What size tubing and spacing are you doing?

    Mad Dog_2
  • Simply Rad
    Simply Rad Member Posts: 209

    1/2” tube @150’ loop length 6” on center.

    Jeffrey Campbell
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,185

    Hi, If the steps were pre-cast, could tubing be placed in the forms and all connected together after the steps were set in place? 🤔

    Yours, Larry

  • hot_rod
    hot_rod Member Posts: 28,078

    Is it outside uncovered, so it sees full snowfall?

    Are both sides of the treads exposed? If so that will be a big load (btu/ sq ft.)

    If not I like Larry's idea and header each tread loop. Exposed on all sides will present a high load on the stairway.

    If you can header each tread consider 1/2" pex. It can bend to a 8D radius, .625 X = 5" radius.

    get 4 runs in a 12" tread. A 12' loop of 1/2"/ pex 110° of 40% glycol, you could run 4.5 gpm

    As you know that front edge melt is crucial. If snow or ice does not melt at the nose of the tread, it is a slip and fall concern. So 1st run 1.5- 2" from nose.

    I think maybe 100 BTU/ sq ft, minimum so you need to get at least 300 btu/ out of the tread!

    If you can get the tread to 100°, 100° tread at 30° ambient 70X 2 btu/ sq ft/ •°∆= 140 btu/hr/ sq ft. You have 3 square feet per tread perhaps?

    I would certainly put some disclaimer on a system if you cannot get adequate BTU to it. At some point YOU need to tell the contractor how it needs to be done :) and what to expect.

    Maybe Lance will add some thoughts

    Screenshot 2025-06-25 at 4.35.52 PM.png

    https://www.phcppros.com/articles/19381-designing-hydronic-snow-and-ice-melting-systems

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2GGross
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,658
    edited June 2025

    This is a job that I would let my competition do. I like giving my competition a job once in a while. Lets them feel important.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    PC7060Alan (California Radiant) Forbes
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,185

    Hi, I'm going to agree with @EdTheHeaterMan . If you cannot make the stairs safe, along with a built-in safety margin, don't accept the job. I might suggest some sort of awning, so snow cannot get to the stairs in the first place. Then add electric heat tape to the stairs and people will want to spend time on them 🤠😁

    Yours, Larry

    EdTheHeaterManMad Dog_2
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,658

    Ok Ok… Lets suppose ypu wantthe rest of the mechanical work at this project, and you have an owner that says "money is no object, how would you do it?" Then I might come up with an aluminum insert that would fit on top of the step. It can be painted or coated with weather proof wear resistant and traction grit to be safe for walking on when wet. This 1" thick insert would have the finish look the owner is looking for in the finished produce but have next to nothing that will keep the heated water from the surface of the step, since the surface of the step is the water holding vessel.

    Screenshot 2025-06-26 at 6.27.47 AM.png

    It's amazing what you can do with aluminum and welding equipment. Of course you will need to pressure test each step insert to 90 PSI for safety reasons to be sure it will hold up under any real conditions that a boiler with a pressure rating of 30 PSI might encounter.

    If the staircase is exposed on one side or both sides, you can design a railing system that will incorporate the connecting piping in the lower section of the railings. If both sides of the staircase are covered in masonry or below grade, than the connecting piping can be placed after the inserts are set in place then insulated, before back fill is added to complete the project.

    That is of course if the building owner really wants to spend the $$$ and you really want the rest of the work.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Member Posts: 28,078

    I'd stay away from aluminum, some day someone may sprinkle ice melt on them. After they get the fuel bill for heating that stairway?

    If aluminum was the final answer, get some extruded aluminum plank, insert tube and pour concrete around them.

    There are a lot of extruded plank designs with no slip surface.

    Screenshot 2025-06-26 at 7.15.46 AM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    EdTheHeaterMan
  • Simply Rad
    Simply Rad Member Posts: 209

    when it’s all said and done these steps are going to cost more than my house. I proposed using watts flex plate to the tube closest to the bull nose. Flex plate is made of graphite and is very thin and conducts heat very well

    Jeffrey Campbell
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,185

    Another thought. Color the concrete dark and put electric radiant heaters above the stairs. 🤠

    Yours, Larry

    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 12,658

    This is for your home…. Can you redesign the step detail to make the snowmelt work better. Like install the insulation closer to the tubing and reduce the bullnose to a manageable projection. You are going to need to live with this design for a long time and pay for the fuel to operate the system. I might look at this as a redesign.

    Screenshot 2025-06-26 at 1.42.00 PM.png

    Just one idea.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Member Posts: 28,078

    Electric mat in each step? A modulating control for energy savings :)

    I'm not sure a suspended slab like that will get warm enough?

    Wind across it and around it will really drive up the load. Same as the wind effect on a driveway SIM, but you have 4 exposed surfaces. And some vertical concrete "risers?

    IR heat above it is not a bad idea @Larry Weingarten A long CoRaVac tube

    Screenshot 2025-06-26 at 3.34.06 PM.png Screenshot 2025-06-26 at 3.33.56 PM.png
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Simply Rad
    Simply Rad Member Posts: 209

    Ed

    This is definitely not my home. It’s an elaborate 3rd home with form over function. Money doesn’t seem to matter nor do any of my ideas to make the system operate appropriately! Thanks for input. House is almost complete so adding electrical options is not an options. Kinda funny, the owners chose to use air to water HP for the primary heat source inside because “it’s the right thing to do” and then they are using NG to melt the snow instead of shovel. 🤷🏼‍♂️

    Jeffrey Campbell
    GGrossPC7060EdTheHeaterMan
  • hot_rod
    hot_rod Member Posts: 28,078

    Energy, like water and other resources, flows towards money.

    A 3rd home so they use it a few weeks a year, maybe never some years? Typical of many of the large SIM projects in ski town trophy homes.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    PC7060
  • Oldbugsy
    Oldbugsy Member Posts: 4

    Call Therma-HEXX. The 11.5 “ wide hydronic ThermaPANEL was specifically designed for steps. It is capable of snowmelting 8” thick granite slabs, concrete, synthetic decking, Ipe, open grate systems, pedestal mounted surfaces and asphalt. The full size ThermaPANEL is used in everything from high rise ob decks, the North American Missile Defense System to driveways and interior radiant heating and cooling from the ceiling and floor. It is a very high output system.

    www.therma-hexx.com

    Doug_35
  • repleo
    repleo Member Posts: 7

    The stair riser / nosings detail doesn't meet code and is dangerous. Underside of nosings must be curved or sloped with no sharp edges. Somebody with a prosthetic leg could get their toe caught under that lip and pull their prosthesis off. Anybody wearing sandles will tear the top of their foot on the underside of the lip. You may think this is not your problem, but if there is a problem everyone who had anything to do with the steps will get hauled into the law suite.

  • jim s_2
    jim s_2 Member Posts: 118

    Buy them a shovel.

    EdTheHeaterMan
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,875

    Dan introduced us to electrically conductive concrete YEARS ago. Cover the roof with solar PV cells (yeah, I know, peak efficiency at 20%… Not my circus, not my monkies) and use this in the slab.

    Larry WeingartenGGrossEdTheHeaterMan
  • Simply Rad
    Simply Rad Member Posts: 209

    Hi Mark and thanks for the video….i will watch it. Well this is the best I could come up with between the builder and concrete contractor. The slab sensor was placed in an area where the concrete is 8” thick so that will help the stairs melt given the long warm up time of the 8” concrete landings. The things we are doing for the uber wealthy is challenging in so many ways.

    IMG_2703.jpeg IMG_2694.jpeg
    Jeffrey Campbell
    Alan (California Radiant) Forbes
  • Kaos
    Kaos Member Posts: 957

    That doesn't look like a lot of pipe for a pretty big piece of concrete but maybe the most you can get with the layout.

    Both mesh and pipes will work better if raised on chairs above the rigid.