t VHE ^ cold start flame back out the tubes

My VHE 6 installed 1990 if the tem is 110 on the gauge and the boiler starts I get flame out of some tubes I shut it down then back or and it runs fine as long as the temp can stay above 120 degrees any suggestions would help Thank You!
Comments
-
Propane or natural gas?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
i don't know what a vhe 6 is but look for the boiler being scooted and for burners that are damaged or clogged. Some burners have designs that rust out and collapse or are damaged of they aren't set up right. make sure you have enough combustion air, that you don't have a sealed off room around the boiler or an attic fan or something. if it is soot or you don't find either of those things, you need someone that understands combustion.
1 -
I believe the VHE 6 is a 6 section Weil McLain boiler that is vented with AL29-4c stainless steel pipe out a side wall or vertical thru the roof. The combustion air comes from inside the boiler room. I believe that the problems that @mattmia2 mentioned are all possibilities. The reason I asked about Propane is that a flame inside the burner tube happens more often on propane burners when the gas pressure is improperly adjusted.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
VHE very high efficiency boiler
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I wouldn't think boiler temperature has anything to do with "Flame out of some tubes". Are you saying not all burner tubes light the first time? Then it needs service. When was the last time it was serviced? Is there a combustion report around?
From the Homeowner Information Manual.
0 -
It isn't boiler temperature but flue temp, the vent is drafting better when it isn't cold but there is some root cause that needs to be figured out.
0 -
I agree , it needs service .. The roll out is a tell tail sign ..Do you notice any soot ? Draft inducer may be weak , when was the last time it was changed ? … Thinking cold boiler.
There was an error rendering this rich post.
0
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 116 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 109 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 984 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements