My VHE 6 installed 1990 if the tem is 110 on the gauge and the boiler starts I get flame out of some tubes I shut it down then back or and it runs fine as long as the temp can stay above 120 degrees any suggestions would help Thank You!

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,948

    Propane or natural gas?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • mattmia2
    mattmia2 Posts: 18,399

    i don't know what a vhe 6 is but look for the boiler being scooted and for burners that are damaged or clogged. Some burners have designs that rust out and collapse or are damaged of they aren't set up right. make sure you have enough combustion air, that you don't have a sealed off room around the boiler or an attic fan or something. if it is soot or you don't find either of those things, you need someone that understands combustion.

    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Posts: 12,948
    edited June 2025

    I believe the VHE 6 is a 6 section Weil McLain boiler that is vented with AL29-4c stainless steel pipe out a side wall or vertical thru the roof. The combustion air comes from inside the boiler room. I believe that the problems that @mattmia2 mentioned are all possibilities. The reason I asked about Propane is that a flame inside the burner tube happens more often on propane burners when the gas pressure is improperly adjusted. 

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • hot_rod
    hot_rod Posts: 28,705

    VHE very high efficiency boiler

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • HVACNUT
    HVACNUT Posts: 7,784

    I wouldn't think boiler temperature has anything to do with "Flame out of some tubes". Are you saying not all burner tubes light the first time? Then it needs service. When was the last time it was serviced? Is there a combustion report around?

    Screenshot_20250616_055200_Drive.jpg

    From the Homeowner Information Manual.

  • mattmia2
    mattmia2 Posts: 18,399

    It isn't boiler temperature but flue temp, the vent is drafting better when it isn't cold but there is some root cause that needs to be figured out.

  • Big Ed_4
    Big Ed_4 Posts: 3,585

    I agree , it needs service .. The roll out is a tell tail sign ..Do you notice any soot ? Draft inducer may be weak , when was the last time it was changed ? … Thinking cold boiler.