Laars blinking green lights of death
jrkeat
jrkeat Posts: 73
edited June 2025 in THE MAIN WALL
I have a Laars Mascot MFTHW120 that I installed in 2020. Except for an occasional quietly recorded fan speed error, it has worked flawlessly. About 2 weeks ago, it failed completely and I got two blinking green lights—one on the front display, and one on the main board, with absolutely nothing on the screen. I had an extra control board (R2080602) around and put it in. Same thing—both LEDs briefly flashing.
But then I left it off for a couple hours and it started up!
Two weeks later, and it has failed again in the exact same way, and lengthy periods of being switched off haven't cured it. I called Laars, and the service guy there said I had a "short" and that is has destroyed both boards. I'm not sure where to go from here. I'm also not confident he is right about the boards being toast, given that the 2nd board didn't work at first and later started working. No fuses on either board have been harmed. I'm not sure what kind of short they could be taking about. The maybe the hot water circulator, the only one that runs right now, has an intermittent short?
I'm not sure where to start with trying to problem solve this. There are no obvious water leaks, burn marks, etc. I could get a new main board, but it seems like it either wouldn't work or would stop working. I could replace every bit of electronics simultaneously and hope that one of them is responsible.
Does anyone have any thoughts or experience with a similar problem?
    mattmia2 Posts: 18,443
    is the power supply part of the board you replaced? sounds like what failed switching power supplies do
    if it is a short, start with everything but power disconnected from the control board and star putting things back one at a time then start looking for shorts in the part that causes the problem to come back. the t-stat wiring or even the t-stat itself if it is electronic is a likely suspect.
  • Big Ed_4
    Big Ed_4 Posts: 3,590
    You have to ohm out the loads . I always ask tech support with a meter in hand ... They would be your best bet they know where to look…. Bring a meter the next time you call :) Good Luck
  • jrkeat
    jrkeat Posts: 73
    I measured most of the connections, didn't find anything obviously wrong, and installed the new board. It has been running for 3 days without a problem. We'll see if it goes the way of the other boards over time.
    109A_5 Posts: 4,786
    edited May 2025
    Are the Green LEDs that were flashing for the sole purpose of indicating 'Power On' and not diagnostics ? If just for 'Power On' indication it sounds like the switching power supply on the control board was hiccuping.
    Switching power supply hiccuping has a few causes, often failing capacitors, another is the power supply is overloaded and fails to start correctly due to the overload. The overload may not damage the power supply. Since the problem occurred with multiple control boards, you could have two bad boards or there is an overload elsewhere in the system. It could be something as simple as a crushed wire causing the intermittent failure.
