Vents for floor drains and similar situations
I am having a midlife crises concerning venting and circuit venting floor drains.
I have always assumed: If the floor drain is in the middle of a room the vent can be connected (at a 45 deg or more above center) and then piped horizontally (below the floor) over to the wall where it can go up vertically. Same with circuit vent for multiple floor drains.
It has been recently pointed out that the dry vent needs to go up 6” above flood level which would put it coming up in the middle of the floor.
Any helpful input?
I can sketch this if it would be helpful.
Comments
-
what code book are you working out of its legal in some code books
0 -
-
in big open rooms , brew pubs, warehouses, etc you can have a combination waste/ vent system designed by an engineer
The one system I did had 3” drain lines reduces to 2” traps so there was air space in the piping for venting
It was in a brew pub with no inside walks to vent up
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@Chuck_17 The above drawing that @hot_rod posts above is an excellent example of traps vented as floor drains.
I'm guessing you are thinking about the term "six inches above flood level rim." That requirement can be established when the trench is dug deep enough to accommodate that measurement. What does the code book say in your area?
0 -
NY State which is basically the 2019 IPC.
The drawing above looks like a typical circuit vented.
The code for Comb Waste and Vent says vent vertically 6" above flood level before horizonal offset. (flood level for floor drains is the floor I assume) Does that mean no horizonatl offset to the wall, or a horizontal offset that other fixture vents may be connected to?
Side question - How do you vent a bank of floor mount water closets?
0 -
-
Side question - How do you vent a bank of floor mount water closets?
Conventional venting on toilets since there’s usually a wall close by. Each one gets its own vent and can be combined once you’re 6” above the flood rim of the fixture.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Here is one example of how to vent floor-mounted water closets.
0 -
Sorry about the blurry pic. but you get the idea.
0 -
Often in public restrooms, toilets that are back to back can share a single vent.
There are other "engineered" options. A SoVent is a single vent system that serves multiple fixtures.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Its where those vents connect in to a branch vent, vent stack or stack vent. The "tie in" needs to be 6" Above Flood Level Rim of the tallest fixtures in that room. As long as you maintain minimum pitch back toward the drain it serves, and respect the sizing charts, you can run quite far before coming up in to a wall or chase. Mad Dog
0 -
Back to back fixture venting is called Common or unit venting. Mad Dog
0 -
Chuck, they do that to keep sketches very simple…Unfortunately, we do the real learnin' on the job and from our elder statement. Mad Dog
1 -
Chuck...all codes that I am familiar with no longer require that a vent take off be at a 45 degree or great which is ideal. As long as the connection is skewed up greater than 95 degrees from the center of the drain, it is acceptable. Mad Dog
0 -
-
-
Distances have gotten much more lenient. NYC up until about 12 yrs ago was each trap requires it's own vent and within in 2 feet...period. now it's 4 feet & they do allow some Wet Venting. Mad Dog
0
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 976 Plumbing
- 6.3K Radiant Heating
- 387 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements