Rinnai E110CRP Error : E 02

Options
2»

Comments

  • 109A_5
    109A_5 Posts: 4,759

    What was the flame current just before it shut down. Was the O2 verified ?

    image.png image.png
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • lindylex
    lindylex Posts: 88

    These are the original symptoms before the re-assembly and after with the new parts. Also this runs occasionally for days without fault for DHW requests.

  • lindylex
    lindylex Posts: 88

    I measured volts and amps at the gas valve during this diagnosis. The amps I did not show in this video. I can check the micro amps and try to see if I can catch it faulting.

    How do I verify the O2?

  • 109A_5
    109A_5 Posts: 4,759

    Combustion analyzer.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • lindylex
    lindylex Posts: 88

    That tool costs to much for me art this time.

    ] Solution Solved [

    After doing the 8000 hours service nothing had changed but it was needed and glad I did it. The only thing left that I narrowed down the issue to was the gas valve. As I showed in the video you can see it open and close multiple times upon a request. When I replaced the valve I noticed that the O-ring on the old one was in very bad shape. This could have been the source of failure causing extra air to enter into the combustion process, not sure. With the new gas valve installed and over a month of data everything is working fine.

    Thanks everyone for your assistance.

    Larry Weingarten